Old 03-23-2011, 06:33 PM   #1
Planning for grounding: new service in new house
A 200A load center will be fed from a feed-through panel in a nearby barn/garage, and we are thinking about how to best do a grounding system.
We need two electrodes, and these, when bonded together and appropriately terminated at the load center, comprise our system. This, per my interpretation of NEC 2008 250.53 (B).
We are thinking that one electrode can be the galvanized steel water line coming from the well (per 250.52 (A)(1)) and the other can be a section of the #4 steel rebar encased in the foundation wall footing (per 250.52 (A)(3)).
We can attach an appropriate copper cable to the rebar before the footing is poured, and stick it out toward the inside, for later attachment at load center.
My question relates to spacing. the water line comes in only 5 or 6 inches above the wall footing. How far apart does code require the cable attachments to these two "electrodes?"
JohnstownFlood is offline   Reply With Quote
Old 03-23-2011, 07:08 PM   #2
joed's Avatar
Rewards Points: 13,766
If this is a NEW house then you may be required to use a UFER ground installed into the foundation. Best verify if your local requires it before you pour the foundation.
Old 03-23-2011, 07:19 PM   #3
Rewards Points: 1,016
Agreed, a ufer is likely required and preferrable - IMO.
Old 03-23-2011, 07:41 PM   #4
But wasn't I describing a Ufer electrode, that being the concrete-encased steel (1/2" diameter) reinforcing bar in the foundation wall footing?
If one electrode is the water pipe, and the other is the Ufer electrode, where does the called for (or is it called for) separation come into play?
The water pipe entry is down near the footing. The Ufer is in the footing.
Old 03-23-2011, 08:08 PM   #5
Master Electrician
Rewards Points: 3,966
There is no spacing requirement.
brric is online now   Reply With Quote
Old 03-23-2011, 08:43 PM   #6
Rewards Points: 1,548
The spacing reqjirement only applies when the grounding electrode is a rod in the earth and when two of them are needed.
They need to be at least 6-1/2 feet apart.
If a ufer ground is required and the concrete pour forgot, omitted, or neglected it, how is that situation resolved? By pouring a dummy footing alongside the foundation after the fact, with a rebar embedded?
Old 03-24-2011, 08:57 AM   #7
Electrician
SD515's Avatar
Rewards Points: 504
6 feet. (Unless the 2011 NEC changed it)
Kyle
Weird wiring in house fdmillion Electrical 13 06-14-2013 06:49 PM
Electrical Service to Guest House cmlewis Electrical 2 12-25-2010 12:29 PM
installing whole house filter on outside of house MikeInFL Plumbing 3 06-12-2010 04:47 PM
Questions about jacking up house to replace rotted rim/sill SolidStateS15 Remodeling 10 03-22-2010 11:43 AM
Complete AC installation in Old Capitol Hill Row House jacko10 HVAC 0 09-18-2007 05:42 PM