Old 05-22-2011, 04:42 PM   #1
E-lec-tri-city
Send a message via ICQ to brons2 Send a message via AIM to brons2 Send a message via MSN to brons2 Send a message via Yahoo to brons2
Pigtails on plugs?
I was told that it was no longer acceptable under code to wire connections to plugs by just hooking the romex to either side of plugs. It was said that you now must use pigtails for all plugs so that the power had a straight-through flow path. Is that correct?
brons2 is offline   Reply With Quote
Old 05-22-2011, 05:00 PM   #2
joed's Avatar
Pigtails on plugs?
Only correct if you are using multiwire circuits. And then only for the neutrals.
Do not PM with questions that can be asked in a forum. I will not respond.
Old 05-22-2011, 05:45 PM   #3
Lic Elect/Inspector/CPO
Pigtails on plugs?
300.13(B) is for multiwire branch circuits
Below is the commentary following 300.13(B):
Grounded conductors (neutrals) of multiwire branch circuits supplying receptacles, lampholders, or other such devices are not permitted to depend on terminal connections for continuity between devices. For such installations (3- or 4-wire circuits), a splice is made and a jumper is connected to the terminal, unless the neutral is looped; that is, a receptacle or lampholder could be replaced without interrupting the continuity of energized downstream line-to-neutral loads (see commentary to 300.14). Opening the neutral could cause unbalanced voltages, and a considerably higher voltage would be impressed on one part of a multiwire branch circuit, especially if the downstream line-to-neutral loads were appreciably unbalanced. This requirement does not apply to individual 2-wire circuits or other circuits that do not contain a grounded (neutral) conductor
NJMarine is offline   Reply With Quote
Old 05-22-2011, 07:52 PM   #4
Missouri Bound's Avatar
Pigtails on plugs?
Regardless of wht you heard, pigtails are by far the best way to wire plugs. It makes them easier to install, and helps eliminate loose connections throughout the circuit.
Old 05-22-2011, 09:24 PM   #5
joed's Avatar
Pigtails on plugs?
That's your opinion. I believe screw terminals are better than nuts. Also in Canada nuts count for box fill.
Old 05-22-2011, 11:11 PM   #6
Pigtails on plugs?
... It makes them easier to install, and helps eliminate loose connections throughout the circuit.
It doesn't aid in eliminating loose circuits. In fact, each splice creates another weak point.
The Following User Says Thank You to sirsparksalot For This Useful Post:
SD515 (05-23-2011)
Old 05-24-2011, 01:22 PM   #7
Chaos Engineer
Big N8's Avatar
Pigtails on plugs?
Believe he is looking at the fact that the wire only makes two connections (wire nuts) that will shut down the circuit rather then four if you mount the wire to both sides of the plug.
Big N8 is offline   Reply With Quote
Plugs used for blown walls bostonbees Insulation 0 05-16-2011 09:52 PM
Weird thing I noticed while changing plugs Red Squirrel Electrical 16 09-01-2009 08:18 PM
KO plugs are dangerous! KE2KB Electrical 10 11-25-2008 07:57 PM
pigtails in Canada rtoni Electrical 13 07-24-2008 12:02 PM
Surge protector that delays power to certain plugs? Thresher Appliances 2 06-24-2008 01:15 PM