Panel Type? - Electrical - DIY Chatroom Home Improvement Forum
Old 08-15-2011, 09:46 PM   #1
Question
Panel type?
If I want a sub panel with more than 6 spots in my attached garage, should I use a main breaker panel or a main lug panel? And can I use either or? I have read if you have more than 6 breakers in your sub. It cannot be main lug. Is this true?
dimyself121 is offline   Reply With Quote
Old 08-15-2011, 09:59 PM   #2
Electrical Contractor
kbsparky's Avatar
If the garage is attached, you do not need a main breaker panel out there.
You can install the largest panel that you want with main lugs only.
-KB
Old 08-16-2011, 12:23 AM   #3
Rewards Points: 506
KB - If the structure is not attached, is a main breaker required?
jlmran is offline   Reply With Quote
Old 08-16-2011, 12:30 AM   #4
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
You will need a mainbreaker if the garage is detached.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 08-16-2011, 07:58 AM   #5
Rewards Points: 506
What is the logic for this requirement?
Old 08-16-2011, 08:33 AM   #6
The codebook
CheapCharlie is offline   Reply With Quote
Old 08-16-2011, 09:13 AM   #7
kbsparky's Avatar
You will need a disconnecting means. The easiest way to accomplish this is to use a main breaker panel.
-KB
Old 08-16-2011, 09:16 AM   #8
electures's Avatar
Detached structures have pretty much the same requirements as a separate service the only thing missing is the meter.
Old 08-16-2011, 07:20 PM   #9
Rewards Points: 506
I live in a rural house. Meter is on a pole and a service disconnect sits immediately below the meter. After the disconnect, the service conductors go back up the pole, and are then suspended overhead to the house where they enter the panel. There is not a main breaker in the panel.
Does this violate the NEC?
Old 08-16-2011, 07:24 PM   #10
electures's Avatar
No. The service disconnect is at the pole. The house has a subpanel.
Old 08-16-2011, 07:37 PM   #11
Rewards Points: 506
Yet the house is not attached to the pole...so why the difference? I'm struggling with the attached/not attached requirements.
EDIT: why can't the main panel serve as the disconnecting means for the panel located in a detached garage?
Old 08-16-2011, 08:31 PM   #12
electures's Avatar
Because the NEC requires a service disconnect at the detached garage.
Old 08-16-2011, 08:38 PM   #13
Rewards Points: 506
And thus the root of my earlier question about the logic of the requirement, not the basis of the requirement.
Old 08-16-2011, 08:53 PM   #14
electures's Avatar
Over the last several code cycles the NEC requirements for detached structures has been tightened up. Currently, detached structures have the same requirements for service requirements as the primary structure, plus the insulated neutral. Minus the meter enclosure. A grounding electrode system has to be established (ground rods). One thing that has to be observed is that the equipment has to be "suitable for use as service equipment". The panel installation instructions will indicate how that is to be done.
Old 08-17-2011, 08:44 AM   #15
I=E/R
a7ecorsair's Avatar
I don't see anything in the thread stating where you will be drawing power to feed your detached garage. Are you planning to draw from the house panel or the pole disconnect?
a7ecorsair is offline   Reply With Quote
More Sub Panel Questions rdkng07 Electrical 6 05-25-2011 09:46 AM
Critique my Sub Panel rjniles Electrical 18 05-18-2011 12:31 AM
sub panel ground and neutral daddyrabbit Electrical 3 01-29-2010 07:49 AM
Melted Service Entrance Wire in Panel theatretch85 Electrical 13 08-22-2008 11:37 AM
Multiple Sub Panel Installation Handyman2007 Electrical 26 12-31-2007 06:47 PM