situation- new construction (no old metal pipes), well-water, plastic pipe entering basement. plumbing is-- a few feet of PEX, branching to copper (for water heater and boiler) and pex distribution throughout the house.
i thought the "main panel" has to be grounded "twice" (as in my old house)-- 1) to the copper water pipe and 2) with a ground-round outside the house.
question is...with plastic pipe entering basement, where is the second ground?
...is one ground rod Ok for the code?
thanks
drgkjd is offline   Reply With Quote
Old 01-17-2012, 10:51 PM   #2
Rewards Points: 13,960
Grounds to water pipes has not been used for a while.
Depending on your local codes on how many ground rods you need.
In VA it's two grounds 6 ft. apart.
drgkjd (01-17-2012)
Old 01-17-2012, 11:42 PM   #3
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
We still use ground from panel to street side of water meter if a copper water line is installed to house and a ground rod bonded to meter socket with grd wire.
If a copper water service isnt available we use the double ground rods
plummen is offline   Reply With Quote
Old 01-18-2012, 07:28 AM   #4
joed's Avatar
Rewards Points: 13,284
The connection to the water line is not a ground. It is a bond. It makes sure the water lines are at ground potential so a short to the water line will not make the pipes live.
The Following 3 Users Say Thank You to joed For This Useful Post:
bob22 (01-18-2012), mpoulton (01-21-2012), Speedy Petey (01-21-2012)
Old 01-18-2012, 08:03 AM   #5
plummen's Avatar
Well the reason we hook the ground to the street side of meter/water service is to ensure there is still a path to ground even if somebody removes the meter to work on something.
And if you attach a ground wire to street side of the water service on a copper or steel or lead water service you still have a ground even if the house/building is plumbed with plastic water lines on the house side of meter
Old 01-18-2012, 09:22 AM   #6
Rewards Points: 1,532
If the water pipe qualifies as a grounding electrode (metal going out 20' underground) it must be part of the grounding electrode system. If not then something else (e.g. ground rods) must be provided as a grounding electrode.
Gas pipes do not qualify as grounding electrodes but the gas plumbing must be bonded to the grounding electrode system (to ground). A gas appliance that uses electricity and that has an equipment grounding conductor (ground wire) will establish the bond from gas plumbing to ground.
Old 01-20-2012, 09:31 PM   #7
Rewards Points: 97
thanks all for your the responses...this is the gist of what i am reading--
1. since there is no water meter and the pipes service-side as well as inside the house are plastic, neither bonding or grounding the plumbing at any point applies here.
2. re ground rods- the local code may require a second rod since there is no water-pipe grounding- so what i need to confirm is : one or two rods?
Old 01-21-2012, 06:37 AM   #8
Licensed electrician
Rewards Points: 1,744
The NEC only requires 10' in contact with the earth, not 20'.
The water line must also be supplemented with another electrode.
plummen (01-21-2012)
Old 01-21-2012, 06:40 AM   #9
Unless you can prove 25 ohms of resistance or less you will require 2 rods. The test equipment is expensive. It is easier to drive two rods and be done with it.
Old 01-21-2012, 07:08 AM   #10
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,968
Yes, but this is ONLY if the pipe is metallic and in contact with the earth for 10' or more. This makes the pipe it self a grounding electrode.
May I ask what you think this "path to ground" is for?
I see this term misused so much I am curious what people think it does.
What do you think the consequences of not having it are?
Old 01-21-2012, 07:43 AM   #11
Rewards Points: 3,256
Ummmm....water will gush everywhere?
Sorry, my odd sense of humor couldn't let this one go.
zappa is offline   Reply With Quote
The Following User Says Thank You to zappa For This Useful Post:
Old 01-21-2012, 07:47 AM   #12
plummen's Avatar
If the house takes a big hit of voltage or a major dead short I want to make it as simple as possible for it to find its way home/to ground!
I consider it a redundent path to ground for the electric service incase the outside ground rod is missing.
Some people think of it as a way of bonding the metal parts of plumbing system,which it also does but if that was the only reason I wouldnt see the need to run it all the way to the street side of service which weve been required to do in these parts for last 30 years ive been doing it
*Around town anyway the majority of our water services are copper or steel/lead,we dont have many plastic water services to deal with except when you get out to some of the farms
Old 01-21-2012, 08:05 AM   #13
This is my point about misconceptions. Voltage is absolutely NOT seeking "ground" like so many people think.
"Home" for the voltage is NOT the dirt outside or anything like it. Home is the utility transformer. The earth is NOT a path for fault current, nor does it have ANYTHING to do with line voltage fault current. The earth or a ground rod will have NO part in clearing that "major dead short" you referred to.
Grounding electrodes are for lightning and high voltage surges, nothing more. This includes a water pipe electrode.
That is exactly the major role. The water pipe BOND. THIS is much more important. That is to clear any faults that might occur on a metallic water line. The fact that the piping system is bonded to the service equipment puts it at the same potential as the service neutral, which is intern bonded to the service equipment via the main boning jumper. Which in turn is a path for fault current to the circuit breaker.
The reason for running it to the street side of the meter is so that the metallic underground pipe can also be used as an electrode, which if it exists MUST be used.
The Following 3 Users Say Thank You to Speedy Petey For This Useful Post:
Jim Port (01-21-2012), mpoulton (01-21-2012), zappa (01-21-2012)
Old 01-21-2012, 08:14 AM   #14
plummen's Avatar
So is the copper or other metal water line leaving the house through the ground not a path to ground just like the ground rod pounded into the ground outside next to meter socket?
Maybe I should use a term other than way back home,such as more convenient location to dispose of a short or fault other than somebodys body?
Old 01-21-2012, 08:22 AM   #15
Exactly.
Fine, if you think a ground rod is helping you trip breaker or clear faults fine. I'll stick to knowing whats correct.
You've been doing this HOW long?
Here is some good reading: http://ecmweb.com/mag/electric_groun...ing/index.html
From the article:
The Following User Says Thank You to Speedy Petey For This Useful Post:
sub panel or main panel grounding dghowery Electrical 1 10-13-2010 09:18 AM
grounding of main panel and sub panel in older house linkysys Electrical 2 10-01-2009 04:34 PM
Garage Wiring issues jimmyfloyd Electrical 20 06-08-2009 02:57 PM
Sub Panel Grounding bar bmancanfly Electrical 12 05-24-2009 02:07 PM
new Main Panel Grounding lrr81765 Electrical 8 10-09-2008 11:16 AM