Hi everyone! I was doing some work outside my house today, and this thought occurred to me. On the outside of my house, directly below the meter, is a 100amp breaker. There are no smaller breakers or circuits branching off of this box, it just goes directly from there to my 200amp indoor breaker box (which I believe is acceptable even though the outside switch is only 100amp). I've never opened up that outdoor breaker to see how it is wired, but it appears to only have space for that one 100amp breaker, and there isn't any space for any other breakers to ever be added.
My question is, since I have that first breaker on the outside, is that actually my main, and my inside breaker box is then a sub panel? There are currently only 3 wires (two insulated, one bare 4 awg copper all jacketed together as SE-U) coming from that outdoor breaker into my indoor breaker box. I was just thinking that maybe that outdoor breaker could be making my indoor breaker box a sub panel, in which case it would really need 4 wires and a split ground and neutral, right?
Hopefully I'm just being paranoid, and the outdoor breaker isn't automatically making my indoor box a sub. I'm looking to sell my house and I want everything to be up to snuff beforehand.
I really appreciate your thoughts! I'm a rare poster, but a frequent reader!
1) I apologize if I'm not using the correct terminology, is the "grounding electrode" the copper ground rod? If so, I'm not sure exactly where it is connected, either to the meter socket or that outside box (again, I haven't opened it). It definitely isn't wired to the panel in the house.
2) If I read the jacket of the wire correctly, all 3 are 4awg. I find that to be rather small, but it looked like that might be ok based on a google search of table 310.15(B)(6)?? Please correct me if I'm misunderstanding that!
I should note that I didn't do any of this wiring, it was like that when I bought the place several years ago. I live in a rural community that had absolutely no licensing or inspections until a few years ago, so who knows if anything was ever right!
And yes, this outdoor breaker shuts off the indoor power, that is its sole purpose. So - if that makes the indoor panel a sub panel, how do I fix the issue?
Well it sounds like youve basically got a 100a service/disconnect feeding a 200a panel.
Do you have a picture of the inside of the panels,what made you start worrying about them?
Well, I'm having trouble sleeping so I just got out of bed and saw your posts. After this one, I'm trying to go back to sleep so don't expect any replies till tomorrow
Plummen: Nothing really made me worry I guess, I just have done a lot of studying of the electrical forums for a garage subpanel project I've been planning at another property, and I got all the info about separating the ground and neutrals on sub panels. Then today out of the blue, I just happened to think about my house electric and how that indoor panel maybe needs another wire. And sorry, I don't have any pictures, I've never even opened up that outdoor box (I'm a little nervous around power I can't shut off). The indoor panel can be safely shutoff outside, but the outside panel can't be shut off without having someone pull the meter. You wanted to know, it is copper 4awg, it says THHN or THWN SE Style U.
Julius: I'm just trying to learn, I'm not questioning your experience, but why does table 310.15(B)(6) indicate that the 4awg copper is acceptable? What I found was 2008 NEC. Am I not understanding correctly when that table should be used?
Apparently I've got a couple of issues at play here - typical! Thanks for the responses so far!
Very good question and the answer is like this. Even though thhn is rated for 90 degrees it can't be used for it in most situation. The reason for that is being that the lugs, circuit breakers Ect.. Are only rated for 75 degrees. Therefore you will be limited to the 75 degree column. Now when using romex you will be limited to the 60 degree column.
Are some of you saying that because I have a meter main, that makes my breaker panel a subpanel? I've never heard that before. My house is only three years old, and I'm pretty sure there aren't four wires feeding the breaker panel. When did that become a requirement? My county was using NEC 2005 when the house was built.
Yes if your house has an outdoor disconnect before the panel(normally done because of distance between meter and panel)the outdoor disconnect is considered the service mains and your panel is considered a sub panel.
If thats the way the house was wired origionally and signed off by city or cty inspector youve got nothing to worry about
Part of the trouble attempting to decipher your situation is the unfortunate fact that the term subpanel is NOT USED in NEC, nor is it defined. For an authoritative discussion about what a subpanel is, and how to spell the term, see http://www.ashireporter.org/articles/articles.aspx?id=1649
While this may be simply an awkward fact of life, the primary issue is that almost everyone in the business seems to think that NEC requires that 4 wire service be extended to subpanels, while three wire service is acceptable for the service disconnect. Of course, NEC does not say this, as NEC does not define subpanel, it clearly cannot specify wire configuration for something that does not exist.
Under article 100, the term panelboard is defined. I think it is relatively clear, or at least as clear as anything in NEC, that a single outside breaker is not a panelboard under the meaning of article 100. Article 408.34 classifies panelboards into Lighting and Appliance Branch-Circuit Panelboards and power panelboards.Your primary panelboard is probably a lighting and applicance branch circuit panelboard under NEC (more than 10% of the overcurrent devices protect lighting and applicance circuits). As such, I believe it requires 4 wire service, since it is not service entrance equipment, however I leave it to the professional electricians to weigh in on this confusing matter.
OK, my house was wired to NEC 2005, which is still the applicable code here. Assuming the service disconnect is 3-wire, is it necessary to run 4 wires to a subpanel in a detached building? If I do, will it hurt anything to connect them all?
Thanks, but that's clear as mud. I have already buried the conduit and run four conductors. Will it hurt anything to hook them all up? There is no permit or inspection for this.
Nope and keep the neutral et ground seperated you may end up buy a ground bussbar for few Euros ( Dollars ) and then you are golden plus sink two ground rods ( if this is a detached building )
Wow, thanks for all the great responses! So it sounds like as long as I leave it alone, I should be grandfathered in on the 3 wire installation, and the 4awg copper is fine.
Now, just for the sake of learning, if I ever were to ever replace this with 4 wire, I understand how to have the breaker panel set up indoors, with the ground and neutral separated. Also, I understand that in the breaker outside, the neutral would come off the lug it has always come off of. My question is, where would I attach the new ground (the 4th wire) at the outside box? I assume there is a small lug of some kind in that outdoor box that the wire attaches to that goes to the ground rod, so would I splice into that wire somehow? What is the method for this, or am I not giving enough details to answer that question?
Again, thank you for all the great posts. It seems like this question may have helped some others besides me!
Dan Holzman was correct in post 18 .... you need a 4 wire feeder from the service disconnect enclosure outside by the meter to the interior 200 amp panel. The one question that still needs to be answered is was the short length of SEU from service equipment to the interior panel inside metal conduit ? Normally the answer is no but .... maybe it is .. ?
NEC 250.24(A)(5) requires separation of neutral and ground load side of the service equipment unless specifically allowed under exceptions in 250.32 and few other areas in the NEC. In your situation they do not apply you need 4 wires or 3 insulated wires and a listed metal conduit between service equipment and the interior panel.
This graphic from mike holt enterprises pretty much sums up what you need
3 wires from the meter to the service equipment .... 4 wires to the downstream panel or if you prefer sub-panel which is not shown.
Thanks Stubbie. I was just getting ready to post a link to that long arse thread about a month ago where you posted all of those really nice diagrams on bonding.
I wouldn't lose sleep over your installation. I've come across several installs like yours that were signed off by inspectors. Most recently was a manufactured home. In your case the neutral in the SEU is carrying both the systems unbalanced current and will also be the effective ground fault path in the event of a ground fault. There is almost no chance of human contact with any objectionable current in your case as there is no parallel path. That usually only occurs when 4 wires are ran and N/G are not separated at the interior panel.
Related Threads
DIY Home Improvement Forum
3.1M posts
319.6K members
Since 2003