Old 08-27-2012, 05:46 PM   #1
Outlets mounted on concrete walls
Ok, so the subpanel is in, lights are all hooked up, 220 saw outlets in....bathroom is wired, sump pump outlet is fixed, its time to run some outlets. So i'm running the circuit with 12-2 NM through the floor joists, but the outlets will be mainly mounted on the walls in metal boxes, so i've got EMT to run down the walls.....any problem using these
at the top, and stripping the sheathing off at the top of the conduit. Otherwise if my calculations are correct I can't run to runs of 12-2 romex in half inch emt........however I can run 6 #12's in half in emt....
ryan50hrl is offline   Reply With Quote
Old 08-27-2012, 05:50 PM   #2
E2 Electrician
stickboy1375's Avatar
The NM jacket has to enter the box and extend by 1/4"... you can use the clamp you posted or they make 1/2" plastic bushings that you just snap on.
Old 08-27-2012, 05:57 PM   #3
Damn....here I was hoping it just had to enter the conduit.... So what would you recommend? I need to get 12/2 into and out of each box to run to the next one.......
Old 08-27-2012, 06:00 PM   #4
E2 Electrician
3/4" emt? or you can nail a board to the wall, or hell, just strap the NM to the concrete, whatever you want to do is all acceptable.
Old 08-27-2012, 06:02 PM   #5
So....I believe ya, just trying to understand the logic behind this.......if its ok to run thhn in conduit, why isn't it ok to stip the sheathing and run just the wires from nm in the conduit? Is it a safety hazard?
Old 08-27-2012, 06:04 PM   #6
E2 Electrician
The cable is a listed assembly, so the jacket must stay intact... its a listing thing, and not tested for what you proposed.
Old 08-27-2012, 06:06 PM   #7
E2 Electrician
Another option you have is to install another box centrally located and run all homeruns from each receptacle location.
Old 08-27-2012, 06:07 PM   #8
Got ya....so if I ran the NM to a junction box at the top, junctioned it with THHN and then ran that down the conduit it'd be fine.....just can't remove the sheathing outside a box....
Old 08-27-2012, 06:08 PM   #9
That might just be the ticket.....I was thinking of doing a few ceiling mounted outlets anyhow for things like sanders and corded drills....
Old 08-27-2012, 06:09 PM   #10
E2 Electrician
Perfect... use big enough boxes to meet box fill and you are golden.
Old 08-27-2012, 06:11 PM   #11
Is the wire in NM THHN? The reason I ask is that I need a few feet of it that will be totally inclosed in conduit to run my dust collector switch, and rather than run out and get some, can I just strip sheathing off of NM?
Old 08-27-2012, 06:15 PM   #12
E2 Electrician
well thats kind of technicality, because we really don't know what the wire type is, there is no label printed on the jacket of the conductors... I know what most guys would do though...
{hint, hint}
Old 08-27-2012, 06:17 PM   #13
Loud and clear.......always to the letter of the code.....
Old 08-27-2012, 06:30 PM   #14
Licensed electrician
Stickboy, check for a change re strapping NM right to the wall. Without looking it now needs protection.
Old 08-27-2012, 06:40 PM   #15
Having trouble understanding why you do not want to sleeve the Romex down the vertical EMT. Its allowed so why do you want to strip the sheathing or run single conductor THHN wire??
hammerlane is offline   Reply With Quote
Putting rigid foam on concrete walls...how to lay DriCore in this setup? ChaoticBliss Building & Construction 14 09-12-2012 06:02 PM
Attaching wood walls to concrete slab Ron55 Building & Construction 11 12-18-2011 08:08 PM
Bamboo on modified concrete pad jhanson Flooring 0 10-08-2011 12:58 PM
Insulating poured concrete basement walls Dude Building & Construction 0 03-03-2010 01:24 PM
Concrete slab with hot water heat- Moving walls skizsam Building & Construction 16 04-06-2009 03:08 PM