dasyckwun 05-30-2012 01:28 PM
outlet help
i bought an air conditoner so i bought a 20amp 250 volt outlet well its a single outlet well my old outlet was a 15amp outlet and had 2black 2white and a ground wire........but this new outlet only needs 3 wires so what ones do i hook up?
bill01 05-30-2012 01:44 PM
none of the above.
You must run new wire. A 15 amp outlet most likely had 14 wire you need 12. You also need a dual pole 20 amp breaker to hook it to.
The wires on that outlet sound like you have power coming in from another outlet or the power panel and a feed going out to the next outlet in the chain. Even if this was 12guage wire you will mess up the whole string of outlets if you were to hook this up to a 20 amp 220 breaker.
Techy 05-30-2012 04:28 PM
You're going to have to run a new dedicated circuit, or get a 120V AC.
Jim Port 05-30-2012 04:32 PM
It might even be a good idea to run a new circuit even if the unit is 120 to avoid tripping due to overloads.
A new circuit is definitely needed for the 240 volt unit.
frenchelectrican 05-31-2012 12:16 AM
As other poster reply the answer to you but let me ask you this one is this window shaker ( window A/C unit ) is really a 240 volt unit ? you may want to double check the nameplate to verify it.
The only time I have see the window shaker that run on 240 volts is pretty big arse unit ( more than 18,000 BTU sizewise ) in stateside.
Merci,