Outlet Box - Electrical - DIY Chatroom Home Improvement Forum
Old 06-02-2011, 05:36 PM   #1
Rewards Points: 27
Outlet Box
I want to run a 20 AMP outlet about 100 feet from the main breaker. Do you think I'd be ok with a 12 gauge wire at that distance or should I go to 10 gauge?
marly
marly is offline   Reply With Quote
Old 06-02-2011, 05:40 PM   #2
12 gauge sounds good!!
Mark30 is offline   Reply With Quote
The Following User Says Thank You to Mark30 For This Useful Post:
marly (06-02-2011)
Old 06-02-2011, 07:29 PM   #3
Lic Elect/Inspector/CPO
12 gauge is fine
NJMarine is offline   Reply With Quote
The Following User Says Thank You to NJMarine For This Useful Post:
marly (06-02-2011)
Old 06-02-2011, 10:39 PM   #4
It depends on what you want to power from that 20 amp outlet. Skill saw, no, reading lamp, no problem.
Tigerloose is offline   Reply With Quote
The Following User Says Thank You to Tigerloose For This Useful Post:
marly (06-03-2011)
Old 06-03-2011, 12:08 AM   #5
Rewards Points: 27
After reading the manual for the device (dust collector) it recommends at least a dedicated 20 amp circuit. After looking at the Voltage Drop Calculator I get a 6.4% drop at 100 feet. They don't have any other specifications, but for them to recommend at dedicated circuit probably means it takes a lot of juice.
It also says that i can wire it for 230V and the voltage calculator says I'll get a 3.2% drop wiring it for 230V.
I guess I can get away with 12 gauge for a 230V, but in the end I'm probably better off running the 10 gauge.
Copper isn't as cheap as it used to be.
marly
Old 06-03-2011, 12:20 AM   #6
Rewards Points: 506
It also says that i can wire it for 230V and the voltage calculator says I'll get a 3.2% drop wiring it for 230V....
marly
Don't know what values you used, but you should input the total distance at 50% of the length of the circuit run. So, for 100 feet, use 50'.
http://www.csgnetwork.com/voltagedropcalc.html
Old 06-03-2011, 08:22 AM   #7
I must have been extra tired last night when I read your original question because I thought it said 200 feet. Anyway, at 100' and 6.4% drop you must be drawing around 10 amps and 10awg is the correct size to keep the voltage within the proper range. Realize that the actual voltage you have may be a bit lower than 120/240 depending on how far away you are from the poco transformer. Another point is that at start-up, motors draw considerably more than the nameplate rating.
Old 06-03-2011, 09:41 AM   #8
Licensed Pro
The circuit length is 100' out and 100' back so 1/2 is 100', not 50.
Old 06-03-2011, 02:19 PM   #9
Rewards Points: 506
I'm sorry, that doesn't make sense to me. She's taking a cable 100' away. If you're talking about the Neutral return back to the panel, then why would the calculator specify anything different?
Old 06-03-2011, 04:53 PM   #10
Sparky
Rewards Points: 510
your 'total circuit length' is your hot+neutral combined
most calculators ask for 'one-way' circuit length
Techy is offline   Reply With Quote
Switched Outlet Issue mjm Electrical 13 06-14-2015 08:56 PM