Old 07-07-2008, 11:38 PM   #1
Outbuilding wiring and underground wiring questions
First off, I am not an electrician, so my apologies in advance for any REALLY stupid statements/question. ;-) I plan on doing research for my project, doing the grunt work, like pulling wires/cables and such, and then letting a licensed electrician review it all, make connections, and power it all up! That said, here's my situation:
I have a 200A main service in the house I bought last year. I also have a 600 SF outbuilding I plan to convert to a small shop/studio. It is about 175 feet from the main panel in the house (in the attic level, actually) The previous owner had the same idea, and already ran a couple PVC conduits from the house to the outbuilding, underground, though I don't know the depth yet. Going by memory here, one conduit is 2" diameter and one is about 3/4" diameter.
My little shop will probably have a table saw, a drill press, a disc sander, scroll saw, and radial arm saw as its main "equipment", along with some shop lighting, maybe a window mounted air conditioner, stereo system/radio, and hopefully, computer capabilities. It will be only me in this shop, so only one "tool" would be running at any one time.
My questions are: How would I determine the wire size for this load and this length of run? Would a 60A sub-panel be adequate? Is PVC conduit OK for this kind of thing, and what depth is required by code?
From my reading, I believe that the panel size is OK, and will require a separate grounding rod bonded to the ground terminal in the sub-panel, and the ground and neutral will need to be separate in the sub-panel as well. Right? Additionally, my GUESS is that romex is the wrong way to go, and that maybe 10/2 wire is OK to pull for this application, on a GFCI from the main panel?? Another post I read said something like "Pull 3, #8 THWN (2 blacks and one white) and a #10 green" for a similar situation?? Was planning on a 12 space/24 circuit panel.
So what have I got right, and what have I got wrong? Any other suggestions/comments are most appreciated.
Thanks again!
tpagel is offline   Reply With Quote
Old 07-08-2008, 01:17 AM   #2
liscenced electrician
if it were me, id pull 2 #6's and a #8 nuetral. Then run bare #6 to 2 ground rods. That would give you 60 amps. To put that in perspective, thats 60 amps per phase, thats a lot of current. Which should be enough for your application, as long as your not going to hook up a big welder or a giant air compressor.
oh and yes pvc is the right thing to use, And i believe its 18 inches for depth, but i always try for 2 feet
jimmy21 is offline   Reply With Quote
Old 07-08-2008, 07:21 AM   #3
I have read that a 60 amp. breaker gives you 30 amps each leg.
BillyD is offline   Reply With Quote
Old 07-08-2008, 07:26 AM   #4
Electrical Contractor
What you read is wrong!
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 07-08-2008, 08:37 AM   #5
Licensed Pro
60A should be plenty, but given the distance I would run #4Cu, or better yet, buy some mobile home feeder (2-2-4-6) Al and save some money. Run this in the larger pipe, and run your phone/cable in the smaller one. You will need ground rods at the shop and an isolated neutral.
Old 07-08-2008, 09:28 AM   #6
So it is a 120 amps 60 amps each leg but will be marked as a 60 amp? 200 amp main does that also mean 400 amps?
Old 07-08-2008, 09:32 AM   #7
Licensed Pro
It is 60A each leg, marked as 60A.
Old 07-08-2008, 09:38 AM   #8
ya, it would just be a 60A 2 pole breaker. 2 pole meaning 2 legs, each one rated at 60A
Running Underground wiring to shop 200Ft kola Electrical 5 06-06-2008 10:13 AM
Underground Wiring millipede Electrical 4 11-24-2006 11:00 PM
'Underground Wiring And Code. michaeltz Electrical 16 12-05-2005 08:58 AM
