For the last 18 months or so I have used nothing but Ideal push-in connectors for wiring connections in J-boxes. They are much easier to install than wire nuts, and, IMO, better for a DIY project in that they are easy to inspect to make sure the wire is installed solidly. I have read up on them, and they use a different connection system than the infamous 'back-stabbed' receptacles. From what I have read, there have been no reports of problems with Ideal connectors. If there is such a report, please post a link because I couldn't find it.

Anyway, one concern that has been raised is that they 'may' not be up to high amp loads. This winter, I ran a 1500W space heater in the basement pretty much 12 hours a day. The circuit was one I ran and connected with Ideals. After the circuit had run for many hours, I opened the J-Box and put a ammeter clamp on the hot wire and got a reading of 14 amps on the circuit. The connectors were cool to the touch and looked exactly the same as the day I had put them in, six months before.

As far as I can tell, these things work as advertised. I know they are rated and approved for connections and are routinely used in new construction residential projects. Please post your opinions on these connectors. Thanks.

Here is a box in my basement with them used for the connections. I used connectors with extra slots so I could add a circuit later.
Attached Thumbnails
Opinions of Ideal push-in wire connectors-505340065_hmcyr-m.jpg  

Bigplanz is online now   Reply With Quote
Old 04-20-2009, 08:09 PM   #2
Resident Electrician
 
Join Date: Apr 2009
Posts: 11
Default

Opinions of Ideal push-in wire connectors


Quote:
Originally Posted by Bigplanz View Post
For the last 18 months or so I have used nothing but Ideal push-in connectors for wiring connections in J-boxes. They are much easier to install than wire nuts, and, IMO, better for a DIY project in that they are easy to inspect to make sure the wire is installed solidly. I have read up on them, and they use a different connection system than the infamous 'back-stabbed' receptacles. From what I have read, there have been no reports of problems with Ideal connectors. If there is such a report, please post a link because I couldn't find it.

Anyway, one concern that has been raised is that they 'may' not be up to high amp loads. This winter, I ran a 1500W space heater in the basement pretty much 12 hours a day. The circuit was one I ran and connected with Ideals. After the circuit had run for many hours, I opened the J-Box and put a ammeter clamp on the hot wire and got a reading of 14 amps on the circuit. The connectors were cool to the touch and looked exactly the same as the day I had put them in, six months before.

As far as I can tell, these things work as advertised. I know they are rated and approved for connections and are routinely used in new construction residential projects. Please post your opinions on these connectors. Thanks.

Here is a box in my basement with them used for the connections. I used connectors with extra slots so I could add a circuit later.
Looks cool but I will never trust any push-in connector. I live and die by wire nuts. Good luck with them. I will keep my good ole tan wire nuts.

thefamouscbc is offline   Reply With Quote
Old 04-20-2009, 08:14 PM   #3
Member
 
Bigplanz's Avatar
 
Join Date: Apr 2009
Location: Louisville KY
Posts: 508
Default

Opinions of Ideal push-in wire connectors


Quote:
Originally Posted by thefamouscbc View Post
Looks cool but I will never trust any push-in connector. I live and die by wire nuts. Good luck with them. I will keep my good ole tan wire nuts.
I understand. I would not presume to give advice to a professional on this matter. However, I do know that our inspectors pass installations made with these because they are 'listed for the use' by UL For a DIY project (non-professional) I believe they are a better choice, in that to ensure the connection is solid, all you have to do is make sure you can see the copper wire in the clear area at the end of the connector. Our inspectors like them too, as they are easy to inspect.

For what it's worth, a Master Electrician I know feels the same way as you, and will used only wire nuts.
Bigplanz is online now   Reply With Quote
Old 04-20-2009, 08:45 PM   #4
Resident Electrician
 
Join Date: Apr 2009
Posts: 11
Default

Opinions of Ideal push-in wire connectors


Quote:
Originally Posted by Bigplanz View Post
I understand. I would not presume to give advice to a professional on this matter. However, I do know that our inspectors pass installations made with these because they are 'listed for the use' by UL For a DIY project (non-professional) I believe they are a better choice, in that to ensure the connection is solid, all you have to do is make sure you can see the copper wire in the clear area at the end of the connector. Our inspectors like them too, as they are easy to inspect.

For what it's worth, a Master Electrician I know feels the same way as you, and will used only wire nuts.
Yeah I agree with you. My thing is with the newbie electricians who do not know how to push the wire all the way in. But with the nuts it is pretty easy to get the connection secure. I wasn't trying to berate you or anything. If done right it is a very secure connection. Sorry if I came off ill. I can get like that sometimes.
thefamouscbc is offline   Reply With Quote
Old 04-20-2009, 09:01 PM   #5
Member
 
Bigplanz's Avatar
 
Join Date: Apr 2009
Location: Louisville KY
Posts: 508
Default

Opinions of Ideal push-in wire connectors


Quote:
Originally Posted by thefamouscbc View Post
Yeah I agree with you. My thing is with the newbie electricians who do not know how to push the wire all the way in. But with the nuts it is pretty easy to get the connection secure. I wasn't trying to berate you or anything. If done right it is a very secure connection. Sorry if I came off ill. I can get like that sometimes.
Your post was fine. I didn't think you were rude at all. I understand your opinion completely. As I said, I would never presume to question the judgment of a professional concerning how they would do their work. Wire nuts are tried and true. Ideals are relatively new, and the back stabbed receptacles gave everyone a bad taste in their mouth about any sort of push in connection. I use Ideals because they work and I can't find any evidence that there has ever been a problem with them in the 'real world.' That's why I am sincere when I say I would like to see a link to a problem, because if I thought there was one i would be down in the basement replacing them ASAP with wire nuts.

For what it's worth, I also like the plastic push in cable clamps. They work great!
Attached Thumbnails
Opinions of Ideal push-in wire connectors-504836191_c4c7a-m.jpg  
Bigplanz is online now   Reply With Quote
Old 04-20-2009, 09:09 PM   #6
Tool Geek
 
PaliBob's Avatar
 
Join Date: Jun 2008
Location: Pacific Palisades CA
Posts: 2,488
Default

Opinions of Ideal push-in wire connectors


Here's another pic of the Ideal 'In-Sure'
http://www.efc-solutions.com/pdf/wireconnectors.pdf

They have been around a while, at least four years

Might be a good idea to pick some up

One area is where you come across a box where some handyman has cut the wires super short.

The Ideal 'In-Sure' should make an easier, faster connection where you can visually verify the contact
__________________
Disclaimer
& Stay Safe
.....Bob Lavery
PaliBob is online now   Reply With Quote
Old 04-20-2009, 09:20 PM   #7
Member
 
Join Date: May 2008
Location: Columbia Heights/NE Minneapolis, MN
Posts: 86
Default

Opinions of Ideal push-in wire connectors


I had no trouble pulling out a push-in connection in my dad's panel that was made with one of those things. It was about as easy as pulling out a push-in connection on, say, a 48 cent P&S single-pole toggle. Just to be safe, I threw it away and replaced it with a wire nut. When I see push-in connections, I think "lazy electrician."

I'm not an electrician, but I am a perfectionist. It annoys me when I see some of the shortcuts some hired professionals make.
thegonagle is offline   Reply With Quote
Old 04-20-2009, 09:29 PM   #8
Member
 
Bigplanz's Avatar
 
Join Date: Apr 2009
Location: Louisville KY
Posts: 508
Default

Opinions of Ideal push-in wire connectors


Quote:
Originally Posted by thegonagle View Post
I had no trouble pulling out a push-in connection in my dad's panel that was made with one of those things. It was about as easy as pulling out a push-in connection on, say, a 48 cent P&S single-pole toggle. Just to be safe, I threw it away and replaced it with a wire nut. When I see push-in connections, I think "lazy electrician."

I'm not an electrician, but I am a perfectionist. It annoys me when I see some of the shortcuts some hired professionals make.
Wire can be pulled out of the connection. They are designed to resist a 'straight pull' but if you hold the connector, then twist the wire with wire pliers and pull at the same time the wire comes out easily. Quite ingenious.

I understand the opinion that they are somehow 'less than.' This opinion is widely shared with those in the profession. What I would like to find out is proof that they are. In my experience (admittedly limited) they have performed quite well, with zero problems of any kind that I have observed.

For what it is worth, I work in Codes and Regulations (not in electrical) and we (Metro Louisville) have approved these for years with no documented failures in any circuit, ever.
Bigplanz is online now   Reply With Quote
Old 04-20-2009, 11:00 PM   #9
Member
 
Join Date: May 2008
Location: Columbia Heights/NE Minneapolis, MN
Posts: 86
Default

Opinions of Ideal push-in wire connectors


Quote:
Originally Posted by Bigplanz View Post
Wire can be pulled out of the connection. They are designed to resist a 'straight pull' but if you hold the connector, then twist the wire with wire pliers and pull at the same time the wire comes out easily. Quite ingenious.
Yes, I had to twist it slightly. My impression was that it was a defect rather than something it was designed to do. It still doesn't make me want to like them more when I see them.

I suppose we'll see how they're still doing in another 20 years. Will they still be working as well as a 30 year old back-stabbed outlet or light switch?
thegonagle is offline   Reply With Quote
Old 04-20-2009, 11:34 PM   #10
Kitchen remodel Guru
 
A.W. Davis's Avatar
 
Join Date: Mar 2007
Location: Bay Area California
Posts: 19
Default

Opinions of Ideal push-in wire connectors


Ive been seeing these wire connectors more prevalant in Halo and other recessed can lights as well. We just cut them off and hard wire all our can lights.
A.W. Davis is offline   Reply With Quote
Old 04-21-2009, 12:00 AM   #11
Member
 
Join Date: Jul 2008
Location: Pennsylvania, USA
Posts: 272
Default

Opinions of Ideal push-in wire connectors


First time I used them, I noticed that the wires would turn inside the connector as I pushed it into the box. Looking inside the connector, the wires are now leaning to the left or right, depending on the way the wire is being stressed from outside the connector. That's not a good feeling for me.

I use them for existing grounds that have been cut short, otherwise I use wirenuts.
__________________
Willis
williswires is offline   Reply With Quote
Old 04-21-2009, 06:11 AM   #12
Member
 
Bigplanz's Avatar
 
Join Date: Apr 2009
Location: Louisville KY
Posts: 508
Default

Opinions of Ideal push-in wire connectors


Quote:
Originally Posted by thegonagle View Post
I suppose we'll see how they're still doing in another 20 years. Will they still be working as well as a 30 year old back-stabbed outlet or light switch?
I had the same concern when I first considered using them. I did a google search and read a spec sheet on the Ideal website and a UL document I found somewhere. The clamping mechanism is evidently of a different design than back stabbed receptacles. Those receptacles have a little slot you push a small screw driver in to release the wire. As I understand it, the Ideal design doesn't have springs in it. The wire will turn in the hole if you twist it, but the internal connection remains solid. Whatever the case, I understand the hesitation about having a possible loose connection. From what I have read, however, this is normal.

One of the reasons I put an ammeter on a connection that fed a space heater was I wanted to see if the connection was warm. It wasn't. There was no evidence of heat, arcing or anything abnormal. If used properly, in a J-box, with strain relief on the cable I have no reservations about using them.
Bigplanz is online now   Reply With Quote
Old 04-21-2009, 07:38 AM   #13
Member
 
Join Date: Jul 2008
Location: Iowa
Posts: 1,543
Default

Opinions of Ideal push-in wire connectors


Remember, the ideal 65 twister was approved by the ul. Just because the ul says its ok, doesn't mean it is. I'm not trying to say these are not solid connections, but I love wire nuts and will stay with them.
rgsgww is offline   Reply With Quote
Old 04-21-2009, 07:52 AM   #14
the Musigician
 
DangerMouse's Avatar
 
Join Date: Jul 2008
Location: I'm right here!
Posts: 10,404
Default

Opinions of Ideal push-in wire connectors


i won't use 'backstabbed spring clip' outlets. found them loose too many times......
but i WILL use what i THOUGHT at first was 'spring clipped' until the wire fell back out and i realised that you had to screw the side screw tight to clamp the wire inside.
twist/wirenut/tape still seems to me to be the most secure for JBs though.

DM
__________________
[SIGPIC][/SIGPIC]Click here to see some of my original magic tricks and trick boxes!
DangerMouse is offline   Reply With Quote
Old 04-21-2009, 08:21 AM   #15
Member
 
Join Date: Jul 2008
Location: Iowa
Posts: 1,543
Default

Opinions of Ideal push-in wire connectors


Who needs to tape their wirenuts?

rgsgww is offline   Reply With Quote
Reply

Tags
electical wiring, ideal connectors, wirenuts


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Adding a wall switch to a pull chain fixture abacuslearns Electrical 17 12-20-2011 06:02 PM
Stove Top wire capt2 Electrical 8 10-05-2007 01:41 PM
Old house, new light fixture, too many wires Persephonee Electrical 3 01-15-2007 08:58 AM
Ideal In-sure Connectors tra999 Electrical 3 10-06-2006 05:25 PM
Does a 6 x 12ga wire nut exist? peeks Electrical 1 10-02-2005 09:58 AM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.