Opinion, would you choose to bury wire or run conduit to shed?
If you were running wire to a shed some 40 feet from the house would you choose to use wire for direct burial or run it in conduit?
I think both will be about the same difficulty, using a pick & mattock it's just as easy for me to make a deep narrow trench for direct burial or use the other side for a trench for conduit so wondering what others would pick (and why). Thanks!
Piedmont is offline   Reply With Quote
Old 05-26-2009, 10:20 AM   #2
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Direct burial is inherently failure prone or damage prone over time. It also requires a deeper trench (24") vs (18") for pvc. IMO pvc with individual thwn conductors is the better of options. Are you running a feeder to a sub-panel or branch circuit of 15 or 20 amps to the shed? If a branch circuit with max protection of 20 amps and gfci protected at it's beginning only 12" deep is required regarless of method.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 05-26-2009, 10:25 AM   #3
Location: Fieldbrook, California for 40 years; retired to Atascadero, California
danandbevsfarm
Personally, Piedmont, for that short a run, I always prefer conduit, It doesn't add a tremendous amount more to the project but adds a whole lot more security that your power line will not leak due to a curious gopher, mole, or even a rock impingement. You didn't say what size wire you were running but if you use conduit allow air space around the NM wiring. Example: 12/2 w/g in at least 1 inch conduit or 10/3 w/g in 1 1/4" or bigger. Dan
danandbevsfarm is offline   Reply With Quote
Old 05-26-2009, 11:10 AM   #4
UAW SKILLED TRADES
Stubbie's Avatar
You CANNOT run NM wiring in conduit underground!! It is not rated for wet locations.
Stubbie
Old 05-26-2009, 11:10 AM   #5
Licensed Pro
OOPS! You cannot use NM wiring in buried conduit, it must be THWN individual conductors or UF (but why bother with UF).
I would opt for PVC conduit and THWN conductors. That will give you many more options in the future and better protect the wiring.
Old 05-26-2009, 11:15 AM   #6
Rewards Points: 410
Thanks all, sounds like conduit is the way to go!
I haven't figured out yet what size wire I need, I'm teetering on a subpanel or not since my current panel is pretty full.
When all said & done I will need 120 ft of wire from the breaker to the shed (with 40 ft under ground) and want it to supply a double-spotlight on the shed, a light inside the shed, and an outlet inside and outside the shed and be able to power an electric lawnmower with a 100 ft extension cord. I'm thinking a 20A breaker will do it, and conduit. What size wire do I need for 120 ft run (plus 100 ft of extension cord for my lawnmower)?
Old 05-26-2009, 11:25 AM   #7
Rewards Points: 502
For all my DIY projects, I always use conduit.
Mainly for the added protection/security of the line being damaged.
-Andrew
DIY hobbiest
AndrewF is offline   Reply With Quote
Old 05-26-2009, 11:26 AM   #8
electrician
It's only a shed. Just bury some UF cable 12 inches down on a 20 amp GFCI breaker and call it a day. The wire size will depend upon the current requirements of an electric lawnmower. What kind of current does an electric mower take?
Silk is offline   Reply With Quote
Old 05-26-2009, 11:38 AM   #9
I've used conduit everywhere
UF inside the shed & under my deck
Old 05-26-2009, 12:58 PM   #10
Rewards Points: 410
It draws 12 amps.
Old 05-26-2009, 01:16 PM   #11
Rewards Points: 128
Originally Posted by Piedmont View Post
It draws 12 amps.
You can see you are already getting close to a 20 amp circuit just with the mower. Are you positive you will not need more power out there down the road?
If it were my shed, it would have a 60 amp sub panel fed with 1" conduit and individual THWN conductors. 4 wires.
Keep in mind you have to dig this trench. Why not cover your bases now. It would be a shame if you realized later on that you did not have enough power out there.
I might even go 1-1/2" conduit just to be sure. This way you could use larger wires if it ever becomes an issue. PVC is cheap, and wire is at a good price right now. Check wire prices at the supply house too.
Have you thought about renting a trencher? I would at least get a price.
Old 05-26-2009, 02:25 PM   #12
I ran a direct burial UF to my garage about a year and a half ago. If I had to do it again, I'd run it in PVC.
A 30" Ditch Witch chain drive trencher was about $140 for 4 hours from a local equipment rental house. That included a trailer, their "damage waiver," and tax. I don't really know if that's a good price or not, but that's what I paid.
thegonagle is offline   Reply With Quote
Old 05-26-2009, 06:09 PM   #13
PVC is so inexpensive, it would be stupid to use direct burial.
220/221 is offline   Reply With Quote
Old 05-26-2009, 09:12 PM   #14
Rewards Points: 1,016
Run it in ample sized PVC today - change your mind in the future and then you can just pull bigger wires rather than dig another trench.
I have also found the bottom of the trench is often the hardest to dig, depending on what you are digging through - if 6" not as deep, it's easier to dig.
Then again, if a single 20a circuit is enough for today and expected future needs, I would not go to the extra work and expence.
Old 05-27-2009, 03:06 AM   #15
" Euro " electrician
frenchelectrican's Avatar
Most of my time it pretty much sop to run in conduit and be done with it due in the future that person can able upgrade it anytime without digging up again.
Most case If I have to rent a trencher it typically run for about 150 half day but for me I get contractor special so I go full day for that price espcally if you do multi trenchings { it did happend from time to time }
But only major gothca is if you have rocky soil or super hard soil better off rent a small or mini exvactor that useally run about 250 or so depending on the size.
Merci,Marc
Do I have any more electrical service capacity? (Power for Shed) Magnus357 Electrical 7 10-13-2012 08:52 AM
Wire my Shed mholmen Electrical 8 04-28-2009 12:38 PM
Detached shed/shop rewire gtmatt Electrical 7 05-24-2008 09:40 AM
running uf to shed bobo60 Electrical 12 04-20-2008 01:41 PM
running wire to a detached shed subpanel amakarevic Electrical 9 03-27-2008 05:15 PM