Ont Code Question - Electrical - DIY Chatroom Home Improvement Forum
Old 08-04-2012, 10:19 AM   #1
ont code question
when a service drop runs over a roof what is the clearence height for the drop
tks keith
loair1 is offline   Reply With Quote
Old 08-04-2012, 10:39 AM   #2
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
230.24 Clearances
Service-drop conductors must be located so that they are not readily accessible, and they must comply with the following clearance requirements:
(A) Above Roofs. Overhead service conductors must maintain a minimum clearance of 8 ft above the surface of a roof for a minimum distance of 3 ft in all directions from the edge of the roof.
Exception No. 2: Where the voltage does not exceed 300V between conductors, overhead conductor clearances from the roof can be reduced from 8 ft to 3 ft, if the slope of the roof exceeds 4 in. in 12 in.
Exception No. 3: If the voltage between conductors does not exceed 300V, the conductor clearance over the roof overhang can be reduced from 8 ft to 1.5 ft, if no more than 6 ft of overhead conductors pass over no more than 4 ft of roof overhang, and the conductors terminate at a through-the-roof raceway or approved support. Figure 230-10 230-24Ax3.cdr
Exception No. 4: The 3 ft vertical clearance that extends from the roof does not apply when the point of attachment is on the side of the building below the roof.
{Side Note} Check with your local utility as they may have different requirements
Old 08-04-2012, 10:46 AM   #3
Master Electrician
He in ontario Canada stickboy. I'll go get my code book in a second.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 08-04-2012, 10:47 AM   #4
E2 Electrician
Ah crap.... I always forget to look at OP's location...
Old 08-04-2012, 11:17 AM   #5
Master Electrician
he didn't have one, it was a shortform in the title of the thread. Would be easy to mistake, there's also an ontario in california so i could be wrong but here's the cec rule.
first off contact the power company, they'll tell you what pole the service is coming from and that will dictate where you have to put your service mast.
the cap has to located between 6 and 12 inches above the line insulator.
Snowfall needs to be taken into account, check with your local inspector.
point of attachment has to be minimum 14.8feet(4.5m) maximum 29.5feet(9m)
cannot be within 1m (39.4inches) of a window, door, or porch. Same clearance goes for the conductors.
min height of drip loops above roof is 24 inches
max height of line insulator above roof is 36inches and 59 inches above ubolt holding service mast.
750mm cable must be left out of the mast head for hydro to make their connections
and the million dollar question
12-312 Conductors over buildings
Conductors shall not be installed over buildings unless a deviation has been allowed in accordance with
Rule 2-030.
and rule 2-030 states
2-030 Deviation or postponement
In any case where deviation or postponement of these Rules and regulations is necessary, special permission shall
be obtained before proceeding with the work, but this special permission shall apply only to the particular
installation for which it is given.
which means basically that firemen need ready and full access to the roof. You can't cross more than an overhang of a roof without special permission from the inspector.
Old 08-04-2012, 11:18 AM   #6
E2 Electrician
Bwahhhh... I thought that was a typo for "ONE" code question....
Old 08-04-2012, 11:26 AM   #7
Master Electrician
i'm not sure why he wants to know, the power company does all that, we just put in the mast where they tell us and leave the 750mm or wire hanging out of it.
Old 08-04-2012, 11:28 AM   #8
E2 Electrician
Same here, BUT... sometimes people put new structures under existing installations...
Old 08-05-2012, 08:20 AM   #9
i guess i wasnt clear in my original post. i am in ont canada. i built a shed under the service wires that have only five feet of clearence. the line voltage is 240v. now i may upgrade the service and want to know if that clearence is sufficient by code
tks
Old 08-05-2012, 08:26 AM   #10
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Judging by this response by Andrew...
I would say you are going to have an issue.
Old 08-05-2012, 10:39 AM   #11
Master Electrician
call the inspector, he'll tell you if it's ok, i know that when crossing sundecks and carports you have to have 8.2feet clearance but i don't see anything there for sheds. One phone call or email to esa will tell you everything you need to know.
here's a link to the question form website.
http://esasafe.com/Corporate/con_001.php
The Following User Says Thank You to andrew79 For This Useful Post:
loair1 (08-05-2012)
Basement Remodel - HVAC Code Question buckybadger HVAC 2 08-16-2011 05:34 PM
Stairway wall help.. (Code question) casper129 Building & Construction 6 07-21-2011 04:24 PM
I have one code question which needs to verify. David200888 Electrical 0 12-21-2010 09:21 AM
Question about exposed junction box on floor & code BradG Electrical 9 03-21-2009 11:05 AM
question about code chrissy2008 Electrical 14 02-01-2009 09:48 PM