Old 08-29-2012, 12:54 AM   #1
only able to use half the watts from my generator
I have a 5000 watt generator with a 20 amp 120v nema 5-20r outlet, and a 20 amp 240v nema 6-20r outlet. I can only get a maximum of 2400 watts of 120v power at 20 amps. Is their a way that I can wire a plug to get 120v from the 20 amp 240v side of the generator?
jp79 is offline   Reply With Quote
Old 08-29-2012, 03:26 AM   #2
Semi-Pro Electro-Geek
Rewards Points: 2,944
The generator internally produces two separate 120V 20A circuits that are out of phase, so they can also be used as one 240V 20A circuit. You can only run a maximum of 20A at 120V on each half of the generator. They are usually wired so there is one receptacle on each half of the generator. If there is only one 120V duplex receptacle, then it's likely that the top and bottom of the receptacle are on different circuits so you can run 20A on each. In the worst case, you may have to make a receptacle box that plugs into the generator's 4-wire 240V receptacle.
mpoulton is offline   Reply With Quote
Old 08-29-2012, 05:10 AM   #3
dmxtothemax's Avatar
Rewards Points: 5,372
Yes, you can get 2 x 20 120v circuits !
But to do it safely would require a recepticule box to be made up.
The two hots would come from the nema 6-20.
and the neutral from the 5-20, 120v socket.
An electricain could make one quickly and safely.
dmxtothemax is offline   Reply With Quote
Generator connection Question - Final Plan Apollo67 Electrical 24 01-30-2012 07:44 PM
Can I use a 750 millivolt generator on a 250 - 500 millvolt Gas Valve stanlam HVAC 36 10-14-2011 06:43 PM
portable generator questions--long post daddyrabbit Electrical 19 01-27-2010 07:40 PM
Need Help Honda EU 2000 generator wiring problem rickytz7111 Electrical 10 11-23-2009 09:18 PM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM