-   -   Old UF cable for ground (http://www.diychatroom.com/f18/old-uf-cable-ground-146829/)
carcode 06-12-2012 01:25 PM
Detached garage with two old unused 3 wire 10 gauge no ground UF cables to house in same conduit. Would like to use one for 240V hot and common and the other for ground. Is it OK to tie all three wires together and label it has ground? Will be used for 5 amp grid tie solar inverter line. Plan on using additional ground rod with 6 gauge solar module ground on garage.
electures 06-12-2012 01:51 PM
All conductors of circuit are required to be in the same cable, conduit or raceway. The answer is no.
Jim Port 06-12-2012 01:58 PM
The conductors are also too small to be paralleled.
electures 06-12-2012 02:16 PM
Agreed. And can't be re-identified.