My son has a workshop that's 150 feet from his house. He has 100 amps going into the main house (rural) and 200 amps to an outside panel below the meter (on the house). I would like to run 100 amps to his workshop for him from this outside panel. It seems straight forward to me, but I thought I would get your advice, I read the columns religiously (I'm old). I plan on trenching down 18 inches. Then from the house, running metal conduit 4 feet across and then down (I'm trying to avoid cement that's below the panel/meter. I'd then switch to non metal in the trench from a 90 elbow. THe trench will need to turn a few times to avoid trees/driveway. I will run 2/0 AL 4 single wires (2 hot, neutral,ground) to a subpanel at the workshop. I'll unband the ground and neutral bars, run rods (2) out 6 feet and go down 8 feet with them. From there, I'm good with the workshop wiring. Did I miss anything? I grew up before "neutral" was a necessity, everybody said they were just trying to sell more Cu. Thanks a bunch.
stickboy1375 08-30-2013 07:04 AM
12 Attachment(s)
Neutral was always a necessity. The terminology is what confuses everyone... :)
wirenut1110 08-30-2013 07:11 AM
1) With just 4' across the house, I would just run PVC the whole way.
2) With 2/0 ungrounded conductors, you could go with a 1/0 neutral and a #2 ground. All 4 @ 2/0 would be overkill.
3)If your trench will turn a few times, plus a 90 going in and a 90 coming out, I would just go another 6" and use direct burial wire and just use pipe in and out of the ground. You'll play hell pulling that length and size wire in too many bends.
You mean ground:thumbsup: