Hello All,
Thanks to everyone for your help in advance. Iíve been lurking on this forum for some time and have appreciated all the advice that is presented.
We purchased a 1930ís home a few months ago and have found one surprise after another. We have discovered that our electrical system is out of code and could pose a danger to us. Iíve decided that the only way to really fix everything is to go through a complete rewire of the house and I am in the process of planning that out.
To tell you about the current system:
  • There is an overhead 100 amp service coming to the house. It is connected to the meter base.
  • The meter base has one tap going to the ďmainĒ panel. This is a 100 amp panel that has no additional spaces for additional circuits. All circuits in the panel have 20 amp breakers.
  • There is a second tap from the meter to a ďsubĒ panel. The panel has 2 double pole breakers- one for the A/C and heat, the other for a double oven. There are no additional spaces on this panel.
  • There is a third tap from the meter to a ďsubĒ panel in the garage. It has 2 double pole breakers- one for the hot water heater and the other for the dryer. There are no additional spaces on this panel.
  • The wiring in the home is mostly fabric covered 2 wire in which the insulation is crumbling away. The wiring is run in metal conduit and the conduit is grounded.
  • Part of the kitchen is done in 3/2 romex wire.
  • The house is 1,400 square feet and averages about one outlet per room. It is 2 stories and has an attic and crawl space.
Hereís what I would like to do:
  • Install a true 100 amp main panel and treat the existing panels as sub panels of the new main. This would give me the ability to shut off power to the house from one location. This would be done by an electrician.
  • Change out the sub panel in the garage for a 200 amp panel. This would be done by an electrician. For the time being, I plan on restricting the panel to 40 amps at the main. Run a 2 gauge wire from the new main panel to this panel. I am building the infrastructure to make this a 200 amp house in the future and the 200 amp panel in the garage will eventually serve as the main panel.
  • We plan on remodeling many portions of the house. As we remodel, I plan on taking circuits off of the old ďmainĒ panel and moving them to the 200 amp main panel. Ultimately, I will end up moving all circuits in the house (and creating some new ones) and putting them on the 200 amp panel in the garage. Once all the circuits are moved, I will end up with 1 100 amp main panel and 1 200 amp sub panel (the 200 amp panel will effectively be a 100 amp panel with lots of spaces). With the current load of the house, I donít think we need 200 amps
  • One of the reasons why I like having a main shut off separate from the 200 amp panel is that I can cut off power to the 200 amp panel and work in it. I am nervous about working in a panel with live service wires that I canít shut off.
A few questions for all of you:
1. When pricing out supplies, the salesman at the local electrical supply said that most people run 20 amp circuits these days vs. 15 amp circuits for general use. I would prefer to use 15 amp circuits because I donít need 20 and the 14 gauge wire will be easier to pull than the 12 gauge wire.
2. The salesman suggested that I buy 12/2 Romex with a ground and just pull the jacket off when running through conduit. Iíve read in other places that it is against code to strip the jacket off of Romex. My initial intention was to run THHN through the conduit in the house. Rather than run 2 wire like the current setup, I want to run 3 wires so that the ground is not through the conduit. Whatís the right way to do this?
3. We will be installing new outlets during the rewire. I donít want to knock a bunch of holes in walls (plaster & lathe) trying to tap them off of existing outlets. It will also be difficult to get behind baseboards. What are my alternatives? Is the best option to put the new outlets on new circuits and run Romex via the crawlspace and the attic? Can I cut into conduit in the attic (or crawlspace), install a junction box, and tap the outlet off of that?
4. Can new outlets be in plastic boxes or do they need to be metal because the rest of the system is metal?
As additional info, both my brother in law and father in law will be helping in this project and both have experience in remodeling and wiring. We also have a friend who is a journeyman electrician who we can call in a bind, but heís not a good enough friend to pull into the major work of this project.
All thoughts and opinions are appreciated.
finnimus is offline   Reply With Quote
Old 01-03-2009, 11:06 AM   #2
I'm not an electrician, so I can't preach code at you, but I thought with a rewire you were required to run 20amp circuts for electrical outlets (maybe I'm thinking kitchen). I thought 15amps were for light circuts...
Even if not, I would take the extra time and effort as I would assume this would raise the resell value of the house...
Sorry I can't be of much help other than a bump really.. I'm slowly working on my own projects and that takes enough time to research them on their own
s_anthony is offline   Reply With Quote
Old 01-03-2009, 11:27 AM   #3
DIYer
1. I prefer 20 for outlets and 15 for lighting but it's far from a universal preference. A few outlet circuits are required to be 20 but the rest can be 15. If you want 15 then do 15.
2. You are correct that it violates a few code parts to strip the jacket off romex and use the wires as if they were THHN. If you want to do it anyway, call your inspector first and ask him if it's OK.
3. You can install junction boxes anywhere in existing circuits to tap off of them. Don't extend ungrounded 2 wire circuits, just replace all those.
4. Both plastic and metal boxes are fine. All the metal parts need to be bonded together, the only way to get in trouble is if you somehow isolate part of a metal conduit system by using plastic boxes.
Gigs is offline   Reply With Quote
Old 01-03-2009, 03:40 PM   #4
Rewards Points: 204
I would make the existing service a 200 amp lug panel. Then use smaller sub panels as needed. Use a meter main type panel outside. This will be your disconnect for the whole house. In addition it will give you some extra breakers outside for future use.
If you must have the 200 amp panel in the garage, why not make this panel the main panel? If it were me this garage panel would be a 100 amp sub or a 200 amp main.
If you upgrade the 100 amp main to a 200 amp main you will not have to move existing cables. While there are no code violations regarding feeding a 200 amp panel from a 100 amp panel, doesn't it make sense to have the larger panel feeding the smaller panels.
200 amps is the norm for most residential applications. What I mean is why stay with 100 amp when you can easily go to 200 amp. You will have to change it out anyway, right?
By using a meter main outside as your service you get the main for the whole house, plus some additional circuits for outside. A 200 amp meter main consists of a meter base, 200 amp disconnect and some extra breaker slots for outside, all in one enclosure.
Take all suggestions from sales people with a grain of salt. You can use 15 amp circuits and twenty amp circuits. You need to understand what needs 20 amp and what CAN be 15 amp. For simplicity, going with 12/2 for all the receptacles and lighting makes some sense. When I rewired my house I used all 12/2 and 20 amp breakers. But you do not have too.
How do you know you don't need 20 amp receptacles? Some vacuum cleaners will trip a 15 amp breaker.
Your kitchen requires two 20 amp circuits.
No. It's conduit with the NM cable in it, or the cable alone. By all means you can use the existing conduit and run THHN. You can pull a green THHN if you want the EGC (ground wire). How much of the house is in conduit? If the whole house is in conduit use it and tap from j-boxes to feed new devices. Its very easy to pull wires in and out of conduit.
They make boxes designed to be installed after walls are complete. However, I would not use this type if at all possible. You are going to have cut some plaster or wall board one way or the other. So mount your boxes to studs or rafters. With a crawlspace and attic space you can run cables up and down inside the walls.
I would not have two recepts next to each other on different circuits. It does not make sense and could be dangerous. Tap from the existing. You can run NM out of boxes that are fed with conduit, as long as you use the correct connectors.
Yes, you can use plastic. You cannot incorporate plastic boxes into a conduit system without a ground wire, but you can leave metal boxes with NM to the devices.
Maybe a few bucks to the Journeyman could save you much more money than you might expect. Call him and ask if he will help, with pay of course.
This is not a project for the average DIY'er. I highly recommend you get proffesional help. There are so many things to consider, and a journeyman considers them every day. I would think real hard on this.
Have you pulled a permit yet? You need one. The inspector can then give you instructions as to how the jurisdiction requires this work to be performed.
If you decide to go forward you can always come back here for extra help. I know you will need it. I am not saying you cannot do this job. I just think some assistance from a professional would be an excellent idea. Good luck......John
Old 01-04-2009, 09:09 AM   #5
Thanks to everyone for your help so far, especially J.V. (John). I'd like to address some of your comments:
"I would make the existing service a 200 amp lug panel. Then use smaller sub panels as needed. Use a meter main type panel outside. This will be your disconnect for the whole house. In addition it will give you some extra breakers outside for future use."
I never thought of a meter main type panel outside. It's not something I've seen used in many residences in this area. What's the cost of this vs. a traditional panel?
If you must have the 200 amp panel in the garage, why not make this panel the main panel? If it were me this garage panel would be a 100 amp sub or a 200 amp main."
I do intend to make this the main panel once all the circuits are moved. The only reason why there's a panel in the garage now is because the old owners ran out of space on the "main" panel outside. Other than that, there's no real need for a sub-panel in the garage (unless someone here convinces me that it's a good idea). Just for right now, the 200 amp will be used as a sub while the circuits are being transferred over. The reason why I picked the garage for the location of a new panel is that I have found 2 areas where I can create a wiring chase to take new circuits up to the 2nd floor and attic.
"If you upgrade the 100 amp main to a 200 amp main you will not have to move existing cables. While there are no code violations regarding feeding a 200 amp panel from a 100 amp panel, doesn't it make sense to have the larger panel feeding the smaller panels.
The current wires are not in good shape, so I'm afraid we'll end up changing everything out regardless of what location we use. Given that, it's much easier to run new wires from the garage than it is from the current panel location. In the old location, we would be able to change out existing wires, but new circuits would be a lot more time consuming. It makes complete sense to have a larger panel feeding smaller panels, that's why the current 100 amp "main" will only feed the new 200 amp panel for a few months. After that, the setup will effectively be a shutoff feeding the 200 amp panel. I can easily upgrade my main panel to support 200 amps, but I need to have the service upgraded and that's something that I don't think I need right now (and I really can't afford it).
When you say: "What I mean is why stay with 100 amp when you can easily go to 200 amp. You will have to change it out anyway, right?" Do you mean the panel, the service, or both?
"By using a meter main outside as your service you get the main for the whole house, plus some additional circuits for outside. A 200 amp meter main consists of a meter base, 200 amp disconnect and some extra breaker slots for outside, all in one enclosure. "
Thanks for giving me this idea, I'm going to start looking into it.
Based on your advice, I'm going to run 12/2 and 20 amp breakers for the general electrical and lighting circuits. The special stuff (dryer, hot water heater, etc.) will have their respective amperage breakers as well.
Also based on your advice, I am going to run THHN through the conduit and NM Cable for new outlets. I would say that 85% of the house is in conduit. I've been told that you can have at most 3 90 degree bends and still be able to pull wire. Did they follow that rule in these old houses? If the wires were not in conduit, I'd be much more reluctant to take this on. The areas that are not in conduit are the kitchen and half of the garage. Old homeowners did their own wiring in these areas. That wiring will be heavily inspected if not changed out. All of my outlets in the kitchen are wired hot neutral reverse and we've even found a lighting fixture wired backwards. That makes me worried about the work behind the walls. Luckily, the wiring in the garage is exposed and the wiring in the kitchen will be exposed during a remodel.
I have not pulled a permit yet or gone through the process of finding out how to get one. I only want to go through all that trouble if I decide to take this on myself. Otherwise, I'll leave all the permit pulling to my electrician.
Speaking of permits, what's the tipping point for pulling a permit? Rewiring the house? Installing a new panel?
Also a question about the areas for a wiring chase I've found in the garage. One uses a wall shared by a bathroom and a hallway. There is no plumbing running through this wall and there is no threat of water getting behind it. The other area is behind the back wall of the bathtub. Granted we'll have tile, backerboard, and plywood, but there is a small but unlikely chance that water will enter this area. Does this change the type of wiring / protection I will need?
Thanks again for all of your (everyone) help so far. I appreciate the time you have taken to reply to my posts.
Old 01-04-2009, 09:10 AM   #6
When rewiring a house, it is not much more expensive to go with 200 amps instead of 100 amps. And not much more expensive to go with 20 amp circuits than 15 amp circuits.
There are many things which use a lot of wattage (amperage). And when you have regular things on the circuit, then add a high wattage appliance like a vacuum cleaner, the breaker trips if it is only 15 amps.
Then anything which produces heat is a high wattage appliance. Space heaters, hair dryers, kitchen appliances like deep fryer, warming plate, microwave, waffle iron, etc.
Then for outside/garage outlets, you might get an air compressor or shop power tools which are high amperage. If you have one circuit for the garage and have a freezer out there, then also run a compressor, the breaker is going to trip with them both running.
Then you might want a window air conditioner or two and want dedicated 20 amp or more circuits for these.
I've lived in homes with all 15 amp breakers and had frequent problems with breakers tripping. Now my house has all 20 amp circuits and I never have a breaker trip.
Here on page 3 is a list of what amperage some appliances use...
http://rveducation101.com/articles/RVConverters.pdf
Billy_Bob is offline   Reply With Quote
Old 01-04-2009, 09:16 AM   #7
P.S. Most things list the wattage. Here are a few calculators to convert wattage to amps or the other way around. Use those under "Single Phase"...
http://www.jobsite-generators.com/po...lculators.html
Old 01-04-2009, 09:17 AM   #8
Bill Bob, thanks for your reply. It looks like we were replying at the same time. I agree with the advice presented here and will run 20 amp circuits through the whole house for general electrical and lighting.
I'm trying to build the infrastructure for 200 amps. The only things that won't support 200 amps in my current plan are the shutoff and the service to the house. Those will probably change in the future when we get some of the other priorities out of the way. Then again, if I call the electrician out to replace/ install the panels and can save money on service calls and various other fees, I might just have it done at that time.
Old 01-04-2009, 09:25 AM   #9
When you start replacing panels and the like, you may be required to bring your main electrical service up to code. And it is less expensive to get an electrician out once than twice. Then not much more for a 200 amp panel. Check the prices at the store.
I like the 200 amp meter main idea.
Then when owning a house, it can be a money drain! I tend to want to put stuff off due to the high cost. But actually I'm glad I did a lot of stuff years ago. The cost these days is double or triple what it was when I did these things. So factor in that the cost will be higher in the future.
Old 01-05-2009, 07:25 PM   #10
Thanks for your additional advice. We're in a frustrating situation here. We purchased this house because it was in better condition than other houses we looked at. Turns out that it had a lot of problems that didn't come up in inspection and the seller did not mention. However, there's no concrete way to prove the previous owner knew about some of the issues so we have no recourse.
If I were to hire an electrician, how long would the job take? We're in 1400 square feet. 10 Lights, and about 12 outlets, mostly in conduits. There's only 1 3 way switch in the entire house.
Old 01-05-2009, 07:35 PM   #11
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
What kind of conduits? Can you post some pictures? of the panels, meter, and the conduits?
Jamie
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 01-05-2009, 08:25 PM   #12
Learning by Doing
Leah Frances's Avatar
I have not pulled a permit yet or gone through the process of finding out how to get one. I only want to go through all that trouble if I decide to take this on myself. Otherwise, I'll leave all the permit pulling to my electrician. [/COLOR][/COLOR]
The best person to answer this question is your local permit office. Some areas require a permit for anything other than a 'repair' some are more liberal - Only your permit office can tell you what your requirements are.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
Old 01-06-2009, 07:52 PM   #13
Jamie
Jamie,
Here are 3 images of the main panel, the first sub panel, and the outside entrance of the service wire into the garage for the 3rd panel. I can't find my camera at this moment to post pictures of the conduit and the other panel, but will do so as soon as I can.
Thanks.
Old House Rewire-img_0720.jpg   Old House Rewire-img_0721.jpg   Old House Rewire-img_0722.jpg
Old 01-29-2010, 05:31 PM   #14
Your situation sounds very similar to ours. We are going to a complete remodel of an adobe/concrete home. There is very little crawl space in the attic, and no real crawl space under the floor. We need to reground our panel, and run conduit throughout the house.
How much did your rewiring job cost you for the 1200 sq. ft. home?
archsteve is offline   Reply With Quote
Old 02-03-2010, 02:29 PM   #15
finnimus, I also have been exploring the idea of rewiring my house. Surprisingly, we have many things in common about our homes (1930's house around 1400-1500 sqft) and electrical situations (old conduit wiring). I have already done much of the moving around of breaker panels via a licensed electrician. I have a detached garage which is where I moved the meter and service entrance to. I bumped up my amp service to 200 at the garage with a 100 amp subpanel for garage power and 150 amp single breaker for the house. From the garage I ran cable to the house via underground conduit to a 150 amp subpanel, which is where I stopped the work a few years ago.
Recently, I have been replacing the insulation in my attic and realized the poor condition of the wiring and how badly it needs to be replaced. Based on your posts I have few questions and maybe some advice; hopefully we can help each other out a little. You mentioned that you were planning to pull most of the old conductors out of the old armored cabling and replace with THHN, which is definitely the cheaper way to go. However, it seems to me that this would be a very difficult task and have found other chat boards that suggest the same thing. One of the other posters suggested that this would be easy, but I wonder if they thought you had conduit instead of the old armored cable. Just for clarity I have posted a pic of what I mean by armored cable. Is this the type of wiring you have? Usually the conductors in the cable are insulated with a brittle plastic (which is now crumbling off) and a cloth sheathing over that. I've been thinking of replacing all the armored cable with 12/2 romex. In most cases where the cable drops into the walls I believe I can just pull out the cable and pull in the romex at the same time as the cable is not stapled down. Have you done any investigating to see if this is the case at your house? In some cases I do expect to leave the old cabling in the walls and fish in new romex, which I don't expect to be to difficult because I know my house doesn't have insulation or cross braces in the walls. In addition, the metal receptacle boxes are easily removed because they are not nailed to studs, but simple nailed to the walls which are wood planks instead of sheet rock. Is any of this similar to your house?
Last edited by UTremodeler; 02-03-2010 at 02:35 PM. Reason: Forgot the pic, sorry!
UTremodeler is offline   Reply With Quote
replumbing an old house simonfrog Plumbing 7 01-30-2012 04:45 AM
House Ventilation oldgrunt Roofing/Siding 8 11-11-2008 03:22 PM
Patio roof to house attachment question mikemobile Building & Construction 1 09-30-2008 07:51 AM
Grounding for two service entrances to same house. jogr Electrical 18 09-24-2008 10:31 AM
Brick and block house footer question. ourzoo Building & Construction 2 07-01-2006 02:57 PM