Old Hotpoint Elect. Range. How Many Amps? - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 09-17-2011, 08:29 PM   #16
Code05's Avatar
Rewards Points: 1,104
Code05 is offline   Reply With Quote
Old 09-17-2011, 08:31 PM   #17
Rewards Points: 79
I was wrong about a 40 amp version. You guys are right.
CheapCharlie is offline   Reply With Quote
Old 09-17-2011, 08:35 PM   #18
So why the difference with heating equip?
With a 10kW heat strip I have to use 6ga wire and 60 amp breakers. The entire system uses less than this stove, but Im required to have a larger circuit. What gives?
Master of Cold is offline   Reply With Quote
Old 09-17-2011, 08:38 PM   #19
Rewards Points: 79
You could get away with a 50A breaker but you need #6 wire.
Old 09-17-2011, 08:46 PM   #20
Code05's Avatar
Nope. Here the NEC considers the strip heat a continuous load.
10000w/240v=41.6a x 125% =52 amps. 50 amp breaker too small.
Old 09-17-2011, 08:49 PM   #21
Code05's Avatar
HVAC has no demand factor and is considered a continuous load.
Old 09-17-2011, 08:49 PM   #22
Rewards Points: 79
damn CEC and NEC differences
Old 09-17-2011, 08:53 PM   #23
Code05's Avatar
We also get to put more than two receptacles on a kitchen circuit.
Old 09-17-2011, 09:17 PM   #24
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
The rating on the range is based on all top burners on high and the oven heating full bore. When would that ever happen?
Coastal South Carolina
Old 09-17-2011, 09:24 PM   #25
Rewards Points: 79
Doesn't matter when this will happen, you have to calculate your load based on the nameplate and size everything according to the code.
Old 09-17-2011, 09:25 PM   #26
Code05's Avatar
Even if it did, with the elements cycling it would not pull amperage for long.
Old 09-17-2011, 09:30 PM   #27
A "Handy Husband"
rjniles's Avatar
You need to read and understand the sections that Code05 cited about derating:
"Column C of 220.55 says a 8kW demand factor for a 10.6 kW range, so a 40 amp breaker and 8/3 cable would work.
220.18(C)"
Old 09-17-2011, 09:33 PM   #28
Code05's Avatar
The NEC sizes ranges differently.
Old 09-17-2011, 09:41 PM   #29
Code05's Avatar
Here is an article on it.
http://www.ecmag.com/?articleID=8550&fa=article
Old 09-17-2011, 10:30 PM   #30
Rewards Points: 1,192
Name plate rating is based on full possible load. When was the last time you had all top elements and the oven going wide open for more than than 3 hrs.?
bobelectric is offline   Reply With Quote
Moving Electric Range Plug dmartins Electrical 3 11-23-2010 07:48 AM
Had a new electric range installed in my apartment - does this sound right? SAABturboDRIVR Electrical 15 01-02-2010 05:39 AM
yellow flames on Hotpoint Range ajoantmug Plumbing 2 08-06-2009 08:02 PM
Generator as sole power source NGuy Electrical 29 12-20-2008 12:29 AM
Max amps allowed - electrician advice needed Des Electrical 27 06-05-2008 10:31 PM