I purchased an older (probably 12+ years) used electric Hotpoint range to replace a propane stove at a hunting shack. nothing on the name plate says anything about amps. Just says 10.6 killowatts 120/240 and 8.2 killowatts 120/208. Want to put the right gauge copper wire in, as well as correct breaker for the amps? Plenty of power to load center, and run to range location is just shy of 40'.
8/3 with 40 amp breaker or 6/3 with 50 amp breaker?
borrmabd is offline   Reply With Quote
Old 09-16-2011, 08:59 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 252
10.6 kw/240 volt= 44.16 amps, so go with the 50 amp and #6/3 wire.
The Following User Says Thank You to jbfan For This Useful Post:
borrmabd (09-16-2011)
Old 09-17-2011, 04:52 AM   #3
Code05's Avatar
Rewards Points: 1,104
Column C of 220.55 says a 8kW demand factor for a 10.6 kW range, so a 40 amp breaker and 8/3 cable would work.
220.18(C)
Code05 is offline   Reply With Quote
Old 09-17-2011, 07:41 AM   #4
So I could go either way? 50 amp breaker with 6/3 or 40 amp breaker with 8/3? I assume the 40 amp with 8/3 would save $$. Which would be safer? the 250 unit seniors building it came out of were using 50 amp breakers in all the units. Hmm
Old 09-17-2011, 08:00 AM   #5
What kind of plug is on the end of the cable for the range? 40A or 50A? You can't put a 40A receptacle on a 50A breaker.
CheapCharlie is offline   Reply With Quote
Old 09-17-2011, 08:08 AM   #6
It didn't have a plug... so I was going to purchase a 4 prong (not even sure if they come in 40 and 50 amp). I thought I read somewhere that because of the short 6' distance in the cord...40 amp cord works as well?
Old 09-17-2011, 08:31 AM   #7
40A and 50A receptacles are physically different as well. So you have to match them up. But as a previous poster said, use a 50A breaker, 50A plug, 50A receptacle and #6 wire.
BTW, the demand factor from the previous poster is only for calculating a service, not for sizing for the individual appliance.
Old 09-17-2011, 08:35 AM   #8
Awesome. thank you. Hope to be in Manitoba again this year in a week goose hunting.
Old 09-17-2011, 09:48 AM   #9
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
This statement is not correct, you need to read the NEC sections quoted. They very specifically say that the de-rating table is applicable for a single kitchen range appliance.
BTW, you can use a 50 amp receptacle on #8 wire with a 40 amp breaker.
Coastal South Carolina
Old 09-17-2011, 09:54 AM   #10
Master Electrician
Rewards Points: 3,760
Would you please show me a NEMA designation for a 40 amp plug and receptacle.
brric is offline   Reply With Quote
Old 09-17-2011, 09:59 AM   #11
Code05's Avatar
I wanna see it also.
Old 09-17-2011, 01:15 PM   #12
Semi-Pro Electro-Geek
Rewards Points: 2,902
AFAIK, TANSTAAFAR (there ain't no such thing as a forty amp receptacle). Just 30's and 50's. A 40A circuit would use a 50A receptacle. And I'm pretty sure the article quoted specifically applies to kitchen range branch circuit sizing. #8 wire with a 50A receptacle on a 40A breaker would be correct.
mpoulton is offline   Reply With Quote
Old 09-17-2011, 09:05 PM   #13
Nema 14-50
Old 09-17-2011, 09:25 PM   #14
Code05's Avatar
Nema 14-50
Yes that is 50 amp receptacle.
Old 09-17-2011, 09:25 PM   #15
Master Electrician
Nema 14-50
What's your point? that is a single phase, four wire 50 amp receptacle. Where is thwe 40 amp you alluded to?
Moving Electric Range Plug dmartins Electrical 3 11-23-2010 08:48 AM
Had a new electric range installed in my apartment - does this sound right? SAABturboDRIVR Electrical 15 01-02-2010 06:39 AM
yellow flames on Hotpoint Range ajoantmug Plumbing 2 08-06-2009 09:02 PM
Generator as sole power source NGuy Electrical 29 12-20-2008 01:29 AM
Max amps allowed - electrician advice needed Des Electrical 27 06-05-2008 11:31 PM