Old 09-30-2011, 06:23 PM   #1
Is it ok to put line and load in the same conduit?
Hey guys!! Today for my entire 8 hour shift I spent jumping out lights in MC cable. The feeds was done in conduit. On 2 lights in particular, the new lead man had me jump them threw the conduit where the feeds were. I don't think this is code, and I can remember hearing that we don't mix line and load in a raceway so I explained my discomfort with the order that he gave me, but he told me that "it was fine". So I did as I was told, but I think it's wrong, and would like to find the article to support it. Am I making since to you guys, and if so, do you know the article to back me up?
Sunny B. is offline   Reply With Quote
Old 09-30-2011, 06:46 PM   #2
Code05's Avatar
Sunny, other than service conductors, line and load conductors for branch circuits and feeders can share a raceway.
Service, no.
230.7 Other Conductors in Raceway or Cable. Conductors
other than service conductors shall not be installed in
the same service raceway or service cable.
Code05 is offline   Reply With Quote
Old 09-30-2011, 06:46 PM   #3
Licensed electrician
Try looking so you can learn how to use the code book and gain greater familiarity with the rules. Remember, we will help those that help themselves.
What to you think the issue would be if the conduit were shared?
SD515 (09-30-2011)
Old 09-30-2011, 06:52 PM   #4
Well I think it's not a good practice because, if it's a trunk line, let it remain a trunk line. I don't want to confuse the next electrician
Old 09-30-2011, 06:55 PM   #5
Service, no.
Ok well i see that I was wrong, and I just learned something. Thanks Code05!
Old 09-30-2011, 07:00 PM   #6
Code05's Avatar
Sunny, what is a switch loop?
Old 09-30-2011, 07:05 PM   #7
A "switch loop" is when you bring the "feed" into the light, then down to the switch, then back to the light on the "switch leg"
Old 09-30-2011, 07:07 PM   #8
essentially the same thing as you just did. line down to the switch and load back
Techy is offline   Reply With Quote
Old 09-30-2011, 07:07 PM   #9
Code05's Avatar
So, line and load are in the same conduit/cable?
Old 09-30-2011, 07:10 PM   #10
"Laughing" ok your right. I didn't think of it that way. Good point!
Old 09-30-2011, 07:18 PM   #11
Code05's Avatar
You are learning, that is good.
Old 09-30-2011, 09:10 PM   #12
Electrician
SD515's Avatar
Sunny, also look at 300.3(C), (1) & (2). You’ll see that not only can you do what you did today with ‘line & load’, you can have conductors from different panels and voltages, etc. in the same conduit, boxes, equipment, etc. Some limitations of course.
Kyle
The Following 3 Users Say Thank You to SD515 For This Useful Post:
Code05 (10-01-2011), frenchelectrican (10-01-2011), Jim Port (09-30-2011)
trouble with line side and load side wires lenlen1016 Electrical 3 09-03-2010 08:49 AM
reusing breakers tns1 Electrical 24 08-02-2009 12:43 PM
GFCI question: can line and load wires be run inside the same conduit? thegonagle Electrical 32 04-16-2009 07:07 PM
Bathroom circuit: 60V between line and load? Niels Electrical 4 11-30-2008 05:00 AM
Load vs. line wire gvernea Electrical 5 01-16-2008 01:50 AM