Not Sure If It's An Electrical Problem? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-10-2011, 05:07 PM   #1
Question
Not Sure if it's an electrical problem?
My husband installed a 18000 btu window unit and it is cutting off and will only run when the test button on the cord it pushed. He did add a double pole 30 breaker and i'm told it's 12 gauge wire. I'm not sure whether to get a new unit or call an electrician! The unit is only a few years old and It does blow cold when it's on.
Edupree is offline   Reply With Quote
Old 05-10-2011, 06:07 PM   #2
Rewards Points: 512
A test button on the cord?
If it's 12 guage wire, that's too small; you need 10/3 w/ground.
Try and find out from the metal or paper nameplate on the unit what the Current (amperage) requirements are.
Also, if you can, take a pic of the receptacle and the cord and post it here.
Old 05-10-2011, 06:20 PM   #3
licensed electrician
yeah the wire going to the outlet is to small, needs to be 10 AWG but that's not why the pigtail GFCI is tripping, could be a few things, but the one i found most common is a reverse polarity in the receptical, if you have a plug test, make sure the the black and the white aren't reversed any where on the circuit.
The Deez is offline   Reply With Quote
Old 05-10-2011, 06:39 PM   #4
Rewards Points: 512
The Deez is correct in the cause. I've never seen a pigtail GFCI on a cord, but then I'm not that experienced either. Would these connect similar to a GFCI receptical in that the HOT (Black) wire would be attached to a BRASS clip, while the NEUTRAL (White) would be on a (SILVER)? At the very least, it should indicate which is HOT and which is NEUTRAL. ??
Old 05-10-2011, 07:08 PM   #5
I=E/R
a7ecorsair's Avatar
You're getting off base somewhat.
There is no polarity on a 240 volt circuit.
a7ecorsair is offline   Reply With Quote
Old 05-10-2011, 07:33 PM   #6
Household Handyman
Rewards Points: 1,408
I'm with sparksalot: You will need to know/determine the actual amperage draw on this unit under load then determine if you have the actual correct wire size. The GFCI unit on the cord may be determining a slight high amperage draw on the present 12 gauge wiring and shutting this A/C unit down.
Old 05-10-2011, 07:42 PM   #7
Semi-Pro Electro-Geek
Rewards Points: 2,970
Window air conditioners these days have pigtail AFCIs. I think it's rather pointless, but it seems to be a new UL listing requirement or something because they're all doing it. It may be tripping due to an internal problem with the air conditioner. Not sure what external wiring problem could cause the pigtail AFCI to trip. However, as others have mentioned, you need have at least one problem with the circuit: #12 wire cannot be used on a 30A breaker.
mpoulton is offline   Reply With Quote
Old 05-10-2011, 07:45 PM   #8
Double pole refers to the circuit breaker type, not to polarity in the DC +/- sense. A double pole device (switch, breaker, disconnect, relay, etc.) is one that has two separate sets of contacts. All 240V circuits in a 120/240V panel require a double pole breaker, since there are two hots.
http://en.wikipedia.org/wiki/Pole_%2...ct_terminology
Old 05-10-2011, 07:50 PM   #9
I=E/R
a7ecorsair's Avatar
I'm not the one who said the polarity may be wrong. Read post #3.
Old 05-10-2011, 08:08 PM   #10
i missed the 2 pole. in which case reverse polarity obviously isn't the issue. all i can't really think of, it's check the grounding
Old 05-10-2011, 08:18 PM   #11
I=E/R
a7ecorsair's Avatar
Or the pigtail AFCI could be bad. It isn't tripping the breaker.
Old 05-10-2011, 08:54 PM   #12
Yeah, now I get what you mean.
Electrical Problem RSpoto Electrical 12 02-13-2011 01:20 AM
wife tried to fix electrical problem :-\ mikahtx Electrical 14 08-11-2010 01:35 PM
Slight electrical current in bathroom faucet water + other unusual electrical events story Electrical 9 09-16-2009 10:28 PM
Electrical receptacle problem centralhome Electrical 13 12-27-2008 01:45 PM
Electrical "arcing" problem? morden5b Electrical 17 12-17-2008 06:10 PM