no neutral, hot on both sides
Ok I have a strange one here. We have been having a problem at our house that at times the master bedroom will loose power. The breaker does not trip, and other things on that breaker continue to work. This usually happens when something is plugged into the outlet near our door, so I took that outlet apart and all 3 wires going to the outlet were connected wrong and loose, I connected all properly and reinstalled. we had no problems for 2 months. today I installed a new light fixture, very simple install. Removed old lamp attached power wire, neutral wire and ground wire all as they had been connected. Now we are back to square one nothing works in the room at all. I tested with my DVOM and both wires at all the non-working outlets, switches and light fixture have 120volts. Both the neutral and hot wires have 120volts. This is very strange to me, I can't figure it out. The breaker does not blow and the outlets outside the room still work. Any suggestions? Thanks
stingry331 is offline   Reply With Quote
Old 02-27-2011, 03:27 PM   #2
Licensed electrician
Rewards Points: 1,630
Sounds like a loose neutral somewhere in the circuit.
Old 02-27-2011, 03:55 PM   #3
I think you are right I just can't figure out where? Any suggestions on how to find it?
Old 02-27-2011, 03:56 PM   #4
dmxtothemax's Avatar
Rewards Points: 5,366
DITTO !
loose connection somewhere,
Or a faulty cable (broken internally).
dmxtothemax is offline   Reply With Quote
Old 02-27-2011, 04:39 PM   #5
Semi-Pro Electro-Geek
Rewards Points: 2,942
When the problem occurs, check the voltage between neutral and ground EVERYWHERE on the circuit that you can access. Each receptacle, each light fixture, etc. If you find any locations where the neutral does not read 120V to ground, then you know the open neutral is between that device and the rest of the circuit, and that gives you somewhere to start looking.
Since it sounds like the entire circuit may be affected, you might want to check the neutral connection in the panel first.
mpoulton is offline   Reply With Quote
Old 02-27-2011, 06:15 PM   #6
Electrical Contractor
jbfan's Avatar
Rewards Points: 490
Start at the last place you worked.
If it was working correctly for 2 months after you fixed it, and you installed a new light, that has to be where the problem is.
Old 02-27-2011, 06:30 PM   #7
joed's Avatar
Rewards Points: 12,918
If you know how the cabling is routed around the room the problem is in the last working device or the first not working device. Yes that is correct. The problem could be in a working device box.
Old 02-27-2011, 07:18 PM   #8
Thank You everyone for your help. I finally found the problem. I did not know how the wiring was routed so I was having a hard time figuring out which item was the first to not work. I was trying to trace the wiring in the basement. I ended up finding a wire nut connection inside the light switch box in the bathroom was loose. Thanks again for all the help.
Induction Cooktop, no neutral (?!) andersol Electrical 7 09-28-2010 03:47 PM
question on the "stubbie" bonding links n175h Electrical 12 10-13-2009 04:09 PM
Main disconnect neutral wiring Daniel Holzman Electrical 5 10-04-2009 01:36 PM
GFCI feeing subpanel question scott2332 Electrical 45 02-28-2009 03:15 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 04:58 PM