No neutral on A/C disconnect for GFCI
Gurus,
So this is weird. I have a Pullout A/C disconnect as some of you may know from my previous posts/threads and we wired it over the weekend. I installed the 30Amp double pole GFCI breaker because the disconnect is outside. However, there's no neutral on the disconnect. Just the two line in (Hot) and ground lugs. Granted I only used 10/2 wire and was going to run another THWN strand but realized I don't need to do this. I will say though that I used 10/2 UF cable the last 5 feet. Then spliced to Junction box in basement. From there ran the 10/2 NM-B to panel.
So even though I got a GFCI breaker with no neutral attached, I've heard it will still sense a current imbalance or a short? Plus it's 240v whereas GFCI is more for 120v or 120/240v?? I tied the pigtail off the breaker to the neutral lug on panel? Should I just go get a 30A double pole standard breaker, swap them out and save the GFCI?
Thanks,
~S
Skelleyman is offline   Reply With Quote
Old 05-07-2012, 07:57 AM   #2
Code05's Avatar
Rewards Points: 1,104
GFCI protection for the AC unit is not needed. Waste of money. Return if possible.
Code05 is offline   Reply With Quote
The Following User Says Thank You to Code05 For This Useful Post:
gregzoll (05-11-2012)
Old 05-07-2012, 07:59 AM   #3
Licensed electrician
Rewards Points: 1,240
Agreed, there is no requirement or need for the GFI protection on the 240 volt circuit for the A/C.
Yes a GFI will work without a neutral. It is done this way on hot tubs that are straight 240 units.
Old 05-07-2012, 08:01 AM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
An AC compressor does not require GFCI regardless were the disconnect is located.
A 2 pole GFCI does not require a neutral to work, it senses any unbalance between the 2 hot legs.
BTW most current codes call for a 120 volt GFCI receptacle within 15 feet of an outside compressor. For maintenance purposes.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 05-07-2012, 08:04 AM   #5
Code05's Avatar
25 feet. 210.63
The Following 4 Users Say Thank You to Code05 For This Useful Post:
brric (05-07-2012), gregzoll (05-11-2012), NJMarine (05-07-2012), rjniles (05-07-2012)
Old 05-07-2012, 08:12 AM   #6
Rewards Points: 77
Originally Posted by Code05 View Post
25 feet. 210.63
Thanks, There's already a GFCI outlet actually is either 10-15 feet away but well within the 25 foot requirement/code so I'm good there.
Old 05-11-2012, 01:00 PM   #7
Rewards Points: 77
Thanks, so aside from spending the extra $40 for the GFCI breaker, will it suffice or will it be too sensative and trip often for the AC condenser. It's been in about a week and no issues yet. However, we only ran it 30-60 minutes at the complete of the install so the installer could verify and check functionality.
Thanks,
Old 05-11-2012, 03:30 PM   #8
kevinp22's Avatar
it all depends on how much internal leakage the compressor motor has when it starts up. you may not have problems now but as the compressor nears the end of its life it may have issues
An AC compressor operates strictly on 240 volts and so a neutral is not required.
The low voltage wire is a relay that switches the 240 volt power on and off at the unit.
The disconnect switch needs to be a 2 pole and rated for a disconnect.
Personally, I would return that gfci and just make sure the unit and disconnect are properly grounded.
I rewired my house last year and every breaker is GFCI or AFCI except:
AC 2 pole 30 amp
Stove 2 pole 50 amp
refgrigerator dedicated single pole 15 amp\
kevinp22 is offline   Reply With Quote
Bond subpanel Neutral directly to SE neutral using split bolt? Sierevello Electrical 1 01-30-2011 09:08 PM
MWBC bad neutral test results! kbsparky Electrical 15 04-06-2010 09:44 AM
GFCI feeing subpanel question scott2332 Electrical 45 02-28-2009 04:15 PM
Suspected open/loose service neutral mrtomwj Electrical 5 09-28-2006 09:46 AM
Splice in Neutral to Panel - OK or Not? allpraisebob Electrical 4 08-12-2006 06:54 AM