NM Romex In Conduit For Detached Garage?? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-17-2011, 03:03 AM   #1
NM Romex in conduit for detached garage??
Hi. Im running a subpanel to a detached garage. It will be a long 100ft run at 30a 220v. Im planning on using 6/3 romex.
From the main house breaker panel, it will traven through the attic, down the exterior side of the house, underground into the sidewalk/concrete slab, up an exterior brick wall, and into the detached garage. The exterior portions will be covered by 1" PVC conduit.
My question is...
Is it ok to use 6/3 romex wire inside of the pvc conduit? Do i need to use UF, or THHN, or is standard NM ok?
Thanks in advance!
ericht is offline   Reply With Quote
Old 10-17-2011, 04:27 AM   #2
Semi-Pro Electro-Geek
Rewards Points: 2,892
NM is not rated for wet locations, which precludes its use outdoors, in conduit or otherwise. It gets run in underground conduits all the time by people who don't know this, and it fails as a result. The insulation does not do well in constant contact with moisture. Use THWN/THHN.
mpoulton is offline   Reply With Quote
The Following 2 Users Say Thank You to mpoulton For This Useful Post:
Code05 (10-17-2011), ericht (10-17-2011)
Old 10-17-2011, 05:05 AM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
If you only need 30 amps, you can save some money and use #10 IHWN instead of #6.
Coastal South Carolina
The Following 2 Users Say Thank You to rjniles For This Useful Post:
Old 10-17-2011, 06:20 AM   #4
Thanks guys.
So is UF ok to run in coduit?
I only ask because i have "heard" that only individual wires can be ran in conduit, and that cable insulation may cause the wires to overheat. Also, i know it will be a PITA to pull through, but im fine with that.
And im using 6ga wire because of the long run, and to leave room for expansion.
Old 10-17-2011, 06:21 AM   #5
Btw.. what is IHWN..?? I've never seen it locally
Old 10-17-2011, 07:51 AM   #6
Licensed electrician
Rewards Points: 1,240
That should be THWN. It is individual conductors.
Old 10-17-2011, 09:29 AM   #7
Rewards Points: 6,652
Is this a home on slab, or does it have a crawl or basement?
Mpoulton, if that was the case, hundreds of thousands of homes with basements and garages would not have NM in those two spaces.
Old 10-17-2011, 09:41 AM   #8
JOATMON
ddawg16's Avatar
Rewards Points: 1,116
Use #6 THHN/THWN....2 black wires, 1 white wire. Your ground can be a #8 (or 10 I think). In 1", easy to pull. That is exactly what I did to my detached garage. It used to be 3/4"...fit, but was a b!tch to get through.
Even though you think the PVC pipe keeps the wires dry...water still gets in. There are a lot of factors dictating what can and can't be in conduit. There have been a lot of discussions on this board and others about Romex in conduit. I don't think the NEC forbids it....but my county does not allow it. My inspector said that it's not allowed here because of the heat rise. Even though you may be ok space on wire fill, the Romex cover keeps the heat in. Good chance you could exceed the heat rise.
I am personally a big fan of THHN....easy to pull....easy to terminate....
BTW....make sure you don't bond the earth to your neutral in your garage sub panel. And you might want to check...but you will most likley need a ground rod at the garage.
ddawg16 is online now   Reply With Quote
The Following User Says Thank You to ddawg16 For This Useful Post:
ericht (10-19-2011)
Old 10-17-2011, 11:07 AM   #9
A "Handy Husband"
rjniles's Avatar
Typo, meant THWN.
OP, 100' is not a long run so voltage drop is not a real concern. I would run THWN in conduit(first choice) or direct bury UF. I would not run UF in conduit, a real PIA
Old 10-17-2011, 11:33 AM   #10
Code05's Avatar
Rewards Points: 1,104
Typo, meant THWN.
I agree, but OP specifically asked if UF in conduit is legal. It is.
Code05 is offline   Reply With Quote
Old 10-17-2011, 11:37 AM   #11
Code05's Avatar
OP will need 2 if no other electrodes are present. Nobody I know even thinks about trying to test and use only one. Not worth it.
Old 10-17-2011, 11:42 AM   #12
Only in vertical rise or horizontal run for a short distance to protect.
Old 10-17-2011, 12:04 PM   #13
Code05's Avatar
Greg, are you saying I cannot install a complete conduit system and pull UF through the whole run or are you defining where it is is necessary to sleeve the UF from damage?
Old 10-17-2011, 12:14 PM   #14
I am saying that anything jacketed multi-conductor, with the exception of LV such as networking or a/v, should not be ran in conduit. In the case such as when we ran the UF for our garage, it is 3 feet from the sill plate to 18" under the ground. I used emt to protect, then where we have a tree, that we could not go under the roots, but was able to go about 12" under ground, I ran the UF through a short section of about two feet of conduit. Same when we got to the garage, but that section if I recall was about 4 feet.
That is the only time I would use conduit for UF, and if in a basement or garage, would use short enough to protect up to the ceiling for NM. Running conduit is a art, unless you cheat and use el's and t's that you have the screws to hold on emt, or glued for pvc, then I would run straight thhn or thwn depending on the location. I just looked downstairs, and I probably still have a thousand foot each on the spools downstairs of thhn, that I bought when we moved in in 2003. It is nice to keep on hand, especially in that I am going to have to run conduit out front for the porch light, when we put the new awning up. It was one of those things that I should have relocated when I had that section of roof open, but never did.
Old 10-17-2011, 12:22 PM   #15
Code05's Avatar
Greg, I do not like putting large cables in conduit either, my point is that if the OP wants to: he/she can as long as pipe fill and other factors allows it. It is a design choice.
Garage Insulation yamster Insulation 0 07-01-2011 02:30 PM
Running conduit from attic to garage. raptor_demon Electrical 16 01-25-2010 10:12 PM
rewiring garage, questions about conduit pros and cons wombosi Electrical 32 05-08-2009 02:59 AM
Why not Romex in Conduit? Mr Chips Electrical 3 11-08-2008 10:58 AM
Use of unsheathed Romex NM-B wires in conduit? WoodworkerDave Electrical 10 09-29-2008 06:57 PM