NM Cable In PVC Electrical Conduit - Electrical - DIY Chatroom Home Improvement Forum
Old 08-17-2013, 12:32 AM   #1
Rewards Points: 117
NM cable in PVC electrical conduit
I installed a 1.5" diameter 10' piece of the gray PVC electrical conduit on the side of a floor joist in the basement.
I plan on running four 12/2 NM cables through it. Is this OK? Basically using it as a raceway. Both ends are open.
tommyxv is offline   Reply With Quote
Old 08-17-2013, 01:02 AM   #2
" Euro " electrician
frenchelectrican's Avatar
Originally Posted by tommyxv View Post
I installed a 2" diameter 10' piece of the gray PVC electrical conduit on the side of a floor joist in the basement.
I belive it can be ok but the gotcha is the derating due you are bundling them so the derating factor do kick in so you may loose some of the amp capaity rating.
I have to take a look at the NEC code for excat numbers due I am used on French side but for sure you will loose of them unless you put a second one inch PVC conduits then you can able use full rating of the NM cable.
Merci,
marc
Old 08-17-2013, 01:39 AM   #3
Here the update I did check the Art 310.15 (B) (3).(a)
4 to 6 CCC's = 80%
7 to 9 CCC's = 70%
10 to 20 CCC's = 50%
Note : the ground ( bare ou green do not count as CCC's at all ) conductors are not included on this one.
So 4 X 2 NM CCC's = 8 which therfore it will be at 70% rating and my chart for #12 NM at 90C is 25 or 30 amps depending on the chart table it being used ( this is used for derating ONLY .,,, )
So 25 amp X 70% = 17.5 amps.
Or 30 amps X 70% = 21 amps.
NOTE: this is a derated verison so most NM-B cables gernally will have 90C rated conductors but if you have older cable like plain jane NM then it will be restricted to 60C rating so that will pretty much seal it.
But the cable itself is rated 60C for ampacity purpose.
As long it is not hevey loaded you are allright with it.
Merci,
Marc
Last edited by frenchelectrican; 08-17-2013 at 05:21 AM. Reason: add correction on the error on NEC part ( got it crossed with French codes )
The Following User Says Thank You to frenchelectrican For This Useful Post:
Philly Master (08-17-2013)
Old 08-17-2013, 08:00 AM   #4
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Yes, that is acceptable. You might want to consider running four 12-3 cables to get twice as many circuits, the neutrals would not count as current carrying conductors in that application.
Old 08-17-2013, 08:19 AM   #5
Rewards Points: 117
Thank you for all that info. It is all brand new 90C NM cable.
It's actually 1 1/2" conduit.
3 cables are 12/3 for 3 way switches (same circuit)
2 cables are 12/2 for wall receptacles (2 circuits)
Normally I would staple the NM to the side of the joist, but these runs were going over duct work and it was much easier to run it this way. One end up and to 5' of this conduit will be enclosed in a ceiling if that matters.
Old 08-17-2013, 08:20 AM   #6
E2 Electrician
I wouldn't lose any sleep over that installation.
Old 08-17-2013, 08:47 AM   #7
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,990
My question is WHY do this at all??? Cable stackers would look just as good, probably be easier, and also easier to add cables later.
Does it pass though a barrier or wall somehow?
Old 08-17-2013, 08:48 AM   #8
Thing is if this is for home runs then AFCI would likely be required, and we know how easy 2-pole AFCIs are to get, and how cheap they are.
Old 08-17-2013, 09:13 AM   #9
Rewards Points: 117
No, it just goes over duct work (two trunk lines) and the main steel I beam. Getting into your arms, tools, etc in that area to fasten cable or those stackers would be very difficult. Plus I already had the conduit on hand. As long as it's not against code or a fire hazzard, I can deal with it.
Old 08-17-2013, 10:02 AM   #10
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
It is not a raceway, it is a sleeve. No more than four 12/2,s are fine.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 08-17-2013, 10:11 AM   #11
Rewards Points: 117
Thanks for the replies. I will continue to route those cables to thier destinations then. I was waiting to see the responses in case I had to remove the conduit.
Old 08-17-2013, 03:00 PM   #12
E2 Electrician
Old 08-17-2013, 03:29 PM   #13
Rewards Points: 117
Why would I need an AFCI?
Old 08-17-2013, 04:21 PM   #14
E2 Electrician
Depends on what code cycle you are on and what areas the circuits are for.
Old 08-17-2013, 06:47 PM   #15
And these meet code how??
electric cable to detached garage bmorekid Electrical 5 12-31-2011 02:59 PM
Running cable in conduit Audiotekm Electrical 10 11-09-2011 10:46 PM
Spare cable inside conduit...allowed? newguynet Electrical 1 02-18-2011 09:15 AM
electric conduit fred annerino Electrical 2 01-18-2011 10:32 PM
Armored cable run outside in liquid flexible conduit m_driver Electrical 8 07-06-2008 02:15 PM