Inner conductors are type THHN, rated 90 degrees Celsius, 600 volts. Solid strands. Outer jacket is PVC rated at 75 degrees Celsius. Amapcity of the product is limited to that for 60 degrees Celsius
This is about as clear as mud. It does imply that the heat flows from inside to outside but that's not news.
NMC was meant for damp locations. It had a sheath similar to UF cable where the cable jacket surrounded the conductors. It is wasn't meant to be buried in the ground, nor is it sunlight resistant. I haven't seen any NMC that is any newer than maybe the '60s-70s, but it's still in the codebook.
If something like it is needed today, UF-B is used. UF cable can be buried directly in the ground and is approved for wet locations. It can also be used anywhere NM-B can be used, although I don't know why you would want to. (hard to strip)
NM-B is your modern normal indoor wire, what most people call "Romex" Which was /is a brand name. Yes it is made in different colors, so the inspector can see you used 12 awg to wire the kitchen and bath (for example) instead of reading the sheath.