New Sub Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 03-05-2010, 10:40 PM   #1
New Sub Panel
Going to be installing a new sub panel in the attached garage. This panel will be less than 30 feet down the wall. A friend who does electrical work insists that i need a seperate grounding rod and should hook it to the main ground in the primary panel. I know 4 conductors is required, but is it really necessary to have the rod?
angrysmileyface is offline   Reply With Quote
Old 03-05-2010, 10:43 PM   #2
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
no. an attached garage is just like putting a sub in another part of the house. ground and neut are not bonded in the sub (which you appear to be aware of) and there is no other grounding other than the EGC you bring with the feeder.
Old 03-05-2010, 10:46 PM   #3
Is there a specific article in the NEC that states this?
Old 03-05-2010, 10:49 PM   #4
nap
You talking to me?
nap's Avatar
that you don't need a rod? I'm sure there is but I do not know the section off the top of my head.
If the garage was DEttached, then you would install a GE system (rods, water pipe (if present), Ufer, etc.) but in an attached garage, it is just another part of the house.
so, my question to you:
why would you need a rod for an attached garage but not for any other sub installed in a house?
Old 03-05-2010, 10:53 PM   #5
I appreciate the info. I just really need something concrete, and while everything I found supports this concept, Im looking for the scientific/authority on why it extra ground rods are incorrect.
Old 03-05-2010, 11:02 PM   #6
I've never heard of anyone installing another set in an attached structure
Old 03-05-2010, 11:06 PM   #7
nap
You talking to me?
nap's Avatar
then look in chapter 250 of the NEC. It will state where a grounding electrode system is required and a sub-panel in the same building as the main panel is not included in where a GE system is required.
it is incorrect because the code says it is.
A ge system is only installed in a main service disconnect, a detached building, or where you have a separately derived service (such as where you install a transformer withing a building to reduce power from a 277/480 volt supply to a 120/208 volt system) as that would result with a main service disconnect.
Old 03-06-2010, 12:16 AM   #8
Rewards Points: 1,016
From the way you state this, is your friend saying another ground rod is needed at the main panel? If so, not so. Unless maybe he's saying the existing ground at the main panel is incorrect or lacking?
If he's talking a ground at the subpanel in an attached garage, again not so.
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 07:15 PM
100 -> 200 amp panel upgrade questions philipjcaputo Electrical 1 10-30-2009 03:35 AM
Replacing 2 Sub Panels with 1 Larger Panel GuitarJack Electrical 7 08-25-2009 08:43 PM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM