First time homeowner trying to straighten up some out of date wiring in a detached garage. The garage has a 12-3 UF run to an old box with 4 20 amp breakers, two of which were hooked up, 2 not. One circuit for receps, one for lights. The plastic housing on breakers is cracked so they don't snap on tight anymore. I'm starting from scratch within the garage as I'm changing locations of lights and receps. However I am stuck with the feeder as I don't feel like digging up my flagstone patio at this time. Feeder has red, black, and white wires. Red and black to the lugs, white to a neutral bus bar with grounds from receps and lights going there as well. No grounding bus bar present, no ground rods. Whats the safest way to rewire without running a 4 wire feeder? Is the way it was wired before safe?
alscich is offline   Reply With Quote
Old 07-09-2012, 03:48 PM   #2
MarginallyQualified
Rewards Points: 2,464
You're grandfathered in if you leave it all alone.
If the future use is the same (misc L&R in a garage) there should be no reason to need to change anything
If it were my house?
I'd add a ground rod and ground bar and separate the neutrals
Old 07-09-2012, 03:55 PM   #3
Leave it all alone as in not changing out the breakers that are falling apart? Or can I switch out the box and breakers and wire it the same way and be grandfathered in?
Old 07-09-2012, 04:13 PM   #4
MarginallyQualified
Is that what you're asking about? I thought it was the feed/grounding.
If you have a faulty breaker then of course replace that.
One bridge at a time...
Changing anything opens you up to how the inspectors in your town operate.
What you can do at the mechanical level, what will work or not is a different matter.
Old 07-09-2012, 04:19 PM   #5
Thanks for the replies, I'm planning on installing a new sub panel with new breakers due to the condition of the old ones. I guess where I'm uncertain is whether I should install ground rods or duplicate the previous way it was wired.
Old 07-09-2012, 04:32 PM   #6
Licensed electrician
Rewards Points: 1,018
Three wire feeder were allowed under previous editions of the NEC as long as no metallic paths between the building existed like a phone or water line. The neutral was again bonded as a service panel.
You would need to install at least one ground rod or other type of electrode.
Old 07-09-2012, 05:24 PM   #7
Semi-Pro Electro-Geek
Rewards Points: 2,856
Whoa there! You DEFINITELY can't do that. That would leave the grounding system unbonded, which is a disaster waiting to happen. A fault to ground would not trip a breaker, but would electrify the whole grounding system. Unless there is a 4-wire feed with an N-G bond upstream, you MUST bond neutral and ground.
mpoulton is offline   Reply With Quote
Old 07-09-2012, 05:24 PM   #8
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
If you did that, how would a ground fault clear?
Old 07-09-2012, 05:28 PM   #9
E2 Electrician
Hello all,
EDIT, ehhh, nevermind.... forgot you can't extend a non grounded circuit, stick with a small panel, bond the neutral and grounds together, and drive a ground rod.
Old 07-09-2012, 05:33 PM   #10
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
Originally Posted by stickboy1375 View Post
Here is what I would do, scratch the panel all together, now you have a branch circuit not a feeder, I would land the 12-3 UF into a 4" sq. box, install two GFCI's. one fed by the black circuit, one fed by the red circuit, neutrals must be spliced together.... now off the LOAD side of these GFCI's, i would feed the receptacles off the black circuit, keep the lights on the red circuit... now you don't need ground rods. WOO-HOO!!!!
Exactly.
Besides, a 20A feeder is not code complaint. 30A minimum.
Old 07-09-2012, 05:35 PM   #11
E2 Electrician
Originally Posted by Speedy Petey View Post
Exactly.
Sorry Speedy, I edited it because you cannot extend a non grounded circuit... my bad...
Sure it is, only the disconnect has to be rated at 30 amps.
check out 225.39 (B)Rating of Disconnect
The Following User Says Thank You to stickboy1375 For This Useful Post:
jbfan (07-09-2012)
Old 07-09-2012, 06:28 PM   #12
If I do what you suggest with the branch circuit instead of the box and breakers how is it grounded? Or does it not need to be? Thanks
Old 07-09-2012, 06:31 PM   #13
E2 Electrician
You're stuck with the panel my friend, just buy a 2 circuit panel and bond the neutral and grounds together, and drive a ground rod. This really is the only solution for you.
alscich (07-10-2012)
Old 07-09-2012, 06:31 PM   #14
I never even noticed that that was the case.
Old 07-09-2012, 06:35 PM   #15
E2 Electrician
I know, I so missed the non existing grounding conductor...
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 08:15 PM