New Service Ground - Electrical - DIY Chatroom Home Improvement Forum
Old 06-09-2009, 01:59 PM   #1
New service ground
I'm install a new 100 amp service to a detached garage. I'm installing a grounding rod and need to know the proper installion. I've heard tying to the meter, or to service panel through pvc conduit, and various other techiniques on forums. I just want the correct way to ground a new 100 amp service. I have no plumbing at the garage either. Thanks
mark1 is offline   Reply With Quote
Old 06-09-2009, 02:28 PM   #2
Rewards Points: 58
You should use a 4 wire feeder. H-H-N-G. The ground goes to the ground terminal strip in the panel and from there to one or two ground rods. You cannot run the ground (GEC) separate from the feeder. It all must be in one conduit or cable. You need a #8 green or bare and #3 for the hots and neutral, if they are copper. This ground/bonding wire needs to have the same potential as your service bonding grid.
If you are not under the 2008 code cycle 3 wire feeders are allowed. I would still use a 4 wire feeder regardless.
Ps..Connect the ground in the main panel the same way. To the grounding terminal strip.
Old 06-09-2009, 02:34 PM   #3
I'm using #2 copper for 2 hots and 1 neutrals. I used a 5/8 x 8' grounding rod and using a #6 bare ground. When connecting the ground in the panel do I need to separate the neutrals on one side and grounds on the other or do I just connect the #6 bare ground with my #2 copper neutral. Thanks
Old 06-09-2009, 10:55 PM   #4
Licensed Electrician
Magnettica's Avatar
Rewards Points: 150
Send a message via Yahoo to Magnettica
DO NOT connect your neutral and ground wire under the same terminal. These need to be isolated from each other. Your "bare grounds" (EGC's) and neutrals from your branch circuits also need to be isolated. Oversizing your conductors as you have is a good thing, not a code violation.
Good luck.
Union County, NJ, Licensed Electrician
Classic Electric, LLC, Rahway, New Jersey
Magnettica is offline   Reply With Quote
Old 06-09-2009, 11:14 PM   #5
Licensed Pro
The OP says he ran just three wires, which if he is still under the 05 Code and has no other metal pathways, is compliant. In this case the neutral and ground are bonded, just like a service entrance.
Old 06-09-2009, 11:24 PM   #6
You should have 2 hots, a neutral and a #8 ground. Even if you are not under 2008 code, it's the right way to do it.
The ground rod wire and equipment groind from the panel go to a ground bus along with all the groind wires in your garage circuits.
The neutral bus in the garage panel must be isolated from the enclosure and the grounds.
220/221 is offline   Reply With Quote
Old 06-10-2009, 01:01 PM   #7
Rewards Points: 58
OP. Have you already installed the feeder? If you only have three wires, Househelper provided your answer. If you have not installed/buried the feeder, please use 4 wires. H-H-N-G.
If you installed a 3 wire feeder you cannot bring any other metallic pathways from the main service structure to the unattached structure. Metal water lines, Telephone lines and any and all other metallic pathways will be prohibited.
Old 06-10-2009, 05:14 PM   #8
liscenced electrician
Rewards Points: 538
As others have stated the nec recently switched from 3 wire to 4 wires in this situation. Either way you should also drive 2 ground rods
jimmy21 is offline   Reply With Quote
Service entrance ground size ? banks10 Electrical 4 12-18-2008 06:20 AM
Grounding for two service entrances to same house. jogr Electrical 18 09-24-2008 11:31 AM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 12:33 PM
Sub panel grounding sluggermike Electrical 27 11-11-2007 02:23 AM
Subpanel feeder questions Silhanek Electrical 4 03-22-2007 07:30 PM