New Service Drop - Electrical - DIY Chatroom Home Improvement Forum
Old 05-07-2008, 10:12 AM   #1
New Service Drop
I need to run a new 200 amp service line with 3 conductors from pole transformer to a cabin/house about 570' away. The line will be aluminum and due to amp drop will need to be at least 500 MCM. My question is there a jacketed line that can be buried directly saving on schedule 40 conduit and would it be worth it?
The conduit will still be needed for the risers, but if direct bury will pass code in NYS it would save on the labor of threading conduit the full length. Thank you for any feedback you can give.
derby1251 is offline   Reply With Quote
Old 05-07-2008, 10:54 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
Some questions:
-Where are you getting your information from?
-Where are you located?
-What are you basing the 500mcm on? I assume you mean 500mcm aluminum?
Old 05-07-2008, 11:42 AM   #3
Rewards Points: 160
Who's going to hook up your service latteral to the transformer. Not you I hope! Shouldn't the power company be responsible for the latteral? (the conductors from the transformer to your meter panel)? Homeowners and electricians don't make these connections, the POCO does, at least every place I have lived and worked. Now, you may have to pay them if this is a special situation as it seems it is.
Get on the phone with them and get this straight, then let us know what comes of it.
Old 05-07-2008, 05:26 PM   #4
According to National Grid in Western NY, I am responsible for trenching and running the line, once building inspector gives OK, National Grib will then make connections at the pole and meter.
Is there an aluminum service line that can be buried direct without a conduit?
I was told because of distance and voltage drop a gauge of 500MCM, 3 conductor aluminum cable for a secondary direct bury would be needed.
Old 05-07-2008, 06:25 PM   #5
electrical contractor
Rewards Points: 150
Using my voltage drop calculator, to keep under 3% drop you do need to run 500mcm copper, this is for a 200 amp load at a distance of 570 feet with a voltage of 240. This will be very expensive, can the POCO get the transformer closer to you? It is always better to let them come to you if they will.
Jimmy
Life is tough, Life is tougher when you are stupid.
wire_twister is offline   Reply With Quote
Old 05-07-2008, 07:20 PM   #6
In my part of NY they would not likely let you go 570' with secondary. You would need primary to get you within 250' (or less) of the service.
We can go over 250' with larger secondary, but 570' is a LOT over.
Whatever you do, clear it with Nat Grid first.
200 Amp service really needed for a 830 sq ft house? overkill? alexz Electrical 7 11-16-2009 05:54 PM
How can I determine service amperage? dawho1 Electrical 13 04-07-2008 10:10 AM
Pot lights in a drop ceiling Howdy Electrical 3 03-14-2008 08:23 PM
200 amp panel with a 100 amp service? alexz Electrical 10 07-29-2007 10:00 PM
Suspected open/loose service neutral mrtomwj Electrical 5 09-28-2006 08:46 AM