new service
I want to put a new meter box with 200amp breaker it will be 25' from my main panel in the house what size wire will I need between the 2 panels I'm in tn if it matters thanks
mike cook 01-22-2013 03:37 PM
panel
no one have any ideas
eastcoastsparky 01-22-2013 04:06 PM
Are u talkin sub panel or upgraded service
Sent from my iPhone using DIY Forum
mike cook 01-22-2013 04:20 PM
panel
I will be puuting a new meter box with 200 anmp disconect on corner of house about 25' away is the new 200 amp s panel in the house I will be tieing into
eastcoastsparky 01-22-2013 04:27 PM
Ok if its a sub panel use 4/0 AL or 2/0 CU with a #6 CU ground, keep nuetrals anc grounds separate
rrolleston 01-22-2013 04:27 PM
You will need four wires two hots one neutral and a ground after the disconnect to inside and your panel inside will be a sub panel with neutral and ground separate. 4/0 - 4/0 - 2/0 - #4 AL wire will be needed. Will have to be in conduit unless you use 4/0 SER cable. Would require 2-1/2" pvc conduit.
rrolleston 01-22-2013 04:29 PM
2/0 CU is only good for 200 amps when used as a Service entrance conductor. 3/0 CU would be required.
eastcoastsparky 01-22-2013 04:38 PM
I must of had a stupid moment your right, using copper is just dumb. If offers no difference when being used as a feeder. Try bending a piece of 4/0 CU into a lug. Hahahaha!!!!!!!!
rrolleston 01-22-2013 05:40 PM
This is what I use for my electric services when I need a disconnect outside.
Milbank Meter Main with Load Center