The wife and I are about to buy 10 acres which will require getting electricity from the front of the property to the back.
I am looking for ideas for best way to accomplish this, as I would like to have power (100 amp service for RV plus work area/shop) about 750 feet toward the back of the property. I will pay to have the meter and panel installed at the front.....then take it from there.
Above ground or below....if I am doing it myself? I will check price to just have the power run back there initially.....but then would want to have electric up front as well.
More information.....I am in Texas....Leon County is location of property. Any help is appreciated....
rebelliondog is offline   Reply With Quote
Old 05-13-2013, 03:57 PM   #2
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Put the service in the middle, 750' is way to long for secondary conductors....
Old 05-13-2013, 03:59 PM   #3
Special User
Rewards Points: 1,230
I'm no expert, but a back-of-the-envelope calculation says that a 200A service that's 750 feet long will experience considerable voltage drop which will require rather fat (and therefore very expensive) cables. I'm guessing it will be far cheaper to have the POCO run high voltage to the back of your property and install a transformer there to step down to 240V near your home, then run a small branch circuit to the front of the property.
The above post is for entertainment purposes only. Its contents may, and probably will, lead to legal liability and damage or loss of property, life, or limb. Use at your own risk.
tylernt is offline   Reply With Quote
Old 05-13-2013, 04:45 PM   #4
Was thinking the same....so, service in the middle. I should not have any worries with running the 300' or so either direction myself then?
Thanks for the quick replies....
Old 05-13-2013, 04:46 PM   #5
E2 Electrician
300' is still pretty long, but a lot less cheaper than going the whole 750'. The utilities around here will only go 150' secondaries when they are responsible.
Old 05-13-2013, 05:57 PM   #6
Semi-Pro Electro-Geek
Rewards Points: 2,938
Southwire's calculator says that for 3% voltage drop on a 350' run with 100A load, you would need 750kcmil aluminum or 400kcmil copper conductors. That's huge. You really may want to look into having two services, with the POCO running primary in between.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
Philly Master (05-14-2013)
Old 05-13-2013, 05:58 PM   #7
E2 Electrician
Without any ACTUAL load specs, i'd say he is fine, most people couldn't afford a 100 amp electric bill.... i'm willing to bet 250's AL. would suffice, of course, this is speaking blindly without load specs, but if we are talking the average house... i'd say i'm pretty close.
Of course, two services is the best solution if at all possible.
Old 05-13-2013, 06:01 PM   #8
Special User
How much power (amps) do you need at the front of the property? Or, what do you need to power there? Light, welder, etc?
Old 05-13-2013, 07:26 PM   #9
Rewards Points: 150
call the POCO they will help you engineer this.
usair is offline   Reply With Quote
Old 05-14-2013, 06:09 AM   #10
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
I use that one too ... for calulations .. but i got >>>
1 conductors per phase utilizing a #750 Aluminum conductor will limit the voltage drop to 2.95% or less when supplying 100.0 amps for 750 feet on a 240 volt system.
or >>>
1 conductors per phase utilizing a #400 Copper conductor will limit the voltage drop to 2.95% or less when supplying 100.0 amps for 750 feet on a 240 volt system.
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 05-14-2013, 01:25 PM   #11
or >>>
That's because you used 240V. It's actually two 120V runs! If you do the calc using 240V, then the voltage drop observed on the 120V loads can be up to 6% if the load is not symmetrical between the hot legs.
Old 05-14-2013, 01:29 PM   #12
The average load is certainly much less than 100A. But it's the peak load that matters for voltage drop calculations. What happens when the AC starts up? Do the lights blink and the computers reboot?
Old 05-14-2013, 04:32 PM   #13
Rewards Points: 516
My answer is correct .... and it is the SAME. 120v or 240 volts ..
next you used 350' and the OP stated 750' ..
750kcmil aluminum or 400kcmil copper conductors, 120v or 240v, 350' or 750 '
but the answer is still the same any way you slice it ..
Old 05-14-2013, 06:26 PM   #14
E2 Electrician
My lights blink when my ac starts up and i'm pretty close to the transformer, you cannot avoid undersized transformers, the utility rolls that way.
Help with 220 electric range hook up titan7 Electrical 8 04-30-2011 07:39 PM
90 amp electric car charger! The future... Billy_Bob Electrical 16 02-16-2010 02:01 PM
Severe Drainage Issue kirridam Landscaping & Lawn Care 11 07-25-2009 06:44 AM
How do you reseat or put an over door back on??? wvoldwoman Appliances 3 04-19-2009 02:30 PM