-   -   New Panel Installation (http://www.diychatroom.com/f18/new-panel-installation-200506/)
bobbygravelle 05-08-2014 10:11 PM
Hi all
Attached to the house is a panel and attached to that is a sub panel.
What I want to do is run 3/4 PVC, 220v off the sub panel to another panel to a greenhouse. What are some things I need to be aware of/ should know?
I plan on using 10/3 wire off of a breaker on the sub panel
jbfan 05-08-2014 10:16 PM
Unless the 10/3 is uf cable, it can not be used outside.
What is the load of the greenhouse?
bobbygravelle 05-08-2014 10:21 PM
THHN, I am running it in PVC conduit, and lets say the load of the greenhouse is 80 amps ( which would mean I would run a 100 amp panel, correct? )
jbfan 05-08-2014 10:26 PM
Thhn is not allowed in a wet location, must be thwn.
No way you can get 80 amps on #10 wire.
The load at the greenhouse will be limited by thd feed to the first subpanel.
rjniles 05-08-2014 10:41 PM
Originally Posted by bobbygravelle (Post 1347975)
Hi all
What you need to know is that based on your questions you need to hire an electrician.
bobbygravelle 05-08-2014 10:44 PM
Ok thanks,
I haven't checked the wire size feeding the sub panel, but it's a pretty big wire coming in. Let's say it's 2 gauge, which is rated at 130 amps at 90 degrees. Would I have to run this all the way to a new sub panel by the greenhouse?
jbfan 05-09-2014 06:18 AM
With out knowing ALL the details, we can what if until the cows come home!
Philly Master 05-09-2014 06:32 AM
the least expensive way would be to buy #2 Alum. you need 4 wires for a subpanel like this .... its about 1.50 a foot
http://www.homedepot.com/p/Southwire...2801/202316409
you will need 1 1/4" pipe
and FYI for all practical purposes you cannot buy just THHN wire it is all THHN/THWN or dual rated now ...
and the cost would be much higher being that its copper
bobbygravelle 05-09-2014 11:07 AM
Some good answers, thank you
Jim Port 05-09-2014 11:43 AM
The wire cannot be used at its 90 degree ampacity.
sgip2000 05-09-2014 12:00 PM
First, you need to figure out what size load you will have in the greenhouse. Then based on that information, you can figure out the ampacity and wire gauge needed.
bobbygravelle 05-09-2014 06:15 PM
It says that #2 aluminum wire is rated at 90 amps, and I want a 100 amp panel, will I run into problems?
rjniles 05-09-2014 06:36 PM
100 amps to a greenhouse? A grow house?
bobbygravelle 05-09-2014 06:38 PM
yes why
plummen 05-09-2014 08:21 PM
How about a picture of what you have for an existing service including inside the panels, then we can atleast have a clue of what can safely be run.
Thats why I never give estimates over the phone without seeing the job first.:laughing: