New outlets instead of pigtailing
Are there new outlets you can use instead of pigtailing?
Welcome to the forum !! Did your pigtails fall apart? No outlet has to have pigtails? Did you do the pigtailing? Please turn the breaker off! Was it by a cabinet? Is the ceiling fan on high or low? Was the TV on channel 48? help !
You will need to use pigtails on the grounds.
You also need to pigtail the neutrals on a MWBC.
FWIW in Ontario Canada you are required to pigtail the neutral and cannot use the two screws on the receptacle to pass along a neutral in the middle of a run.
I think it is to ensuring higher connection integrity on the neutral. |
The neutral pigtail is sort of a grey area in Canada that the inspectors don't really look for. Depends on how you read the code on whether or not it is allowed. It is an absolute must on a MWBC. And as stated above on a 3 phase system it's a requirement for shared neutrals. |
But usually the problem will still be limited to the J box where the device with the scorch marks is. |
| All times are GMT -4. The time now is 02:46 AM. |