New Main Panel Ground Question - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 06-27-2011, 03:39 PM   #16
Originally Posted by brric View Post
You must have a disconnect at the meter or at the panel unless you intend to have only six breakers in the panel. Normally there is no grounding conductor fromm the meter to the panel as per most utilities requirement--there are exceptions.
I definitely have a disconnect at the panel... but from you experience you don't think that the wire from the main panel to the meter is required...
Interesting.
Since I already have the wire installed, is there any downside to it?
Mironov Central Home Renovation Blog:
www.mironovcentral.blogspot.com
atmironov is offline   Reply With Quote
Old 06-27-2011, 03:42 PM   #17
Master Electrician
Rewards Points: 3,750
You do not splice the wires in the panel. You land them on the proper neutral/grounding buss of the panel. Why is the disconnect not shown in the picture?
brric is offline   Reply With Quote
Old 06-27-2011, 03:42 PM   #18
rbj
Mlo
Originally Posted by atmironov View Post
See picture below. The disconnect is in the Main Panel (Shown as a red box)
Im not even sure what a backfed breaker is... so no, I'm not using one.
What is shown is a Main Lug Only panel that is fed to the lug terminals shown. To use this panel with a disconnect, the main feeder needs to be connected to the main breaker to heat up the phase busses that are essentially backfed. This main breaker needs to be bolted to the frame to make it a listed code compliant installation.
rbj is offline   Reply With Quote
Old 06-27-2011, 03:55 PM   #19
rbj
atmironov, essentially this is not a listed main disconnect panel.
Old 06-27-2011, 03:57 PM   #20
Originally Posted by rbj View Post
What is shown is a Main Lug Only panel that is fed to the lug terminals shown. To use this panel with a disconnect, the feeders need to be connected to the main breaker to heat up the phase busses that are essentially backfed. This main breaker needs to be bolted to the frame to make it a listed code compliant installation.
Yeah, sorry for the confusion... I did install the "bolt in" main breaker. So it does disconnect the phase buses.
This is exactly what I installed
Old 06-27-2011, 04:03 PM   #21
rbj
Okay, so the 100A bolt-on works without modifying the panel.
Old 06-27-2011, 04:07 PM   #22
Master Electrician
Most MLO panels are designed to be field convertible with a main breaker.
Old 06-27-2011, 04:08 PM   #23
Never mind...
Old 06-27-2011, 04:09 PM   #24
So... it looks like it is all wired correctly...
Does the wire need to be connected to the conduit with these?
Old 06-27-2011, 04:10 PM   #25
Master Electrician
Does not your POCO provide specifications for the electrical services that they connect to?
Old 06-27-2011, 04:12 PM   #26
rbj
That may be true after 1960....
Old 06-27-2011, 04:17 PM   #27
Not that I could find... they just say when its signed off by the city they will turn your power on.
Old 06-27-2011, 04:21 PM   #28
rbj
Generally only if it is RMC conduited using over 1 awg conductors.
Old 06-27-2011, 04:24 PM   #29
Master Electrician
So, you just started doing this from the seat of your pants with no prior guidance?
Old 06-27-2011, 04:36 PM   #30
Nope... I read the NEC, the CEC amendments, and the San Francisco Electrical Code amendments.
Unfortunately I can't memorize everything and searching through the code can be pretty difficult if you don't know the exact terminology... So if the only thing I've botched up was not connecting the ground to the conduit, then I think I've done okay... but Ill be sure and let you know after my inspection.
Circuit Panel Question, neutral & ground bars ChrisDIY Electrical 32 02-14-2011 01:01 PM
Subpanel next to Main panel wired the same in 1990 Uncle Wayne Electrical 3 01-20-2011 01:43 AM
grounding of main panel and sub panel in older house linkysys Electrical 2 10-01-2009 05:34 PM
Quick question: No ground bar in panel? dawho1 Electrical 3 04-06-2008 11:17 AM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM