New Main Panel Ground Question - Electrical - DIY Chatroom Home Improvement Forum
Old 06-27-2011, 12:01 PM   #1
Hey Everyone,
I have finished a complete rewire of my place... but before I called for an inspection I had a contractor take a look at my work. Everything looks good except for the way I have the grounding set up.
This first diagram is how I actually have it wired.
And this is a pictures of the actual panel (before I wired it) showing where the main wires would go
After talking with the contractor he stated that my grounding wire needs to be continuous from the wire poured in the foundation, through the main panel, and over to the meter.
He also stated that the ground wire needs to be connected to all the conduit with these:
Furthermore, he said that I need to have an additional grounding rod driven into the ground, and from there run a wire to the main water line then back to the ground wire that is poured into the foundation then back to the meter. Here is a diagram that shows it the best I can.
I believe him on the conduit connections but am not convinced on the continuous wire, or second grounding rod.
Any input would be greatly appreciated.
Also, if a continuous wire is needed... how can you splice #4 AWG copper?
Mironov Central Home Renovation Blog:
www.mironovcentral.blogspot.com
atmironov is offline   Reply With Quote
Old 06-27-2011, 12:09 PM   #2
Licensed electrician
Rewards Points: 1,622
You must have some local amendments. The NEC would only require the UFER ground and the rod electrode would not be needed. The GEC would only need to be continous to the UFER, not to all the electrodes all together.
Some power companies will not allow grounding to take place in the socket.
The connections on the GEC would need to be made in an irreversible manner like a hydraulic crimp or a welded connection like a Cadweld.
Old 06-27-2011, 12:14 PM   #3
Thanks for the Quick Reply Jim.
I just need to clarify a few things.
UFER = Wire Poured in Foundation?
GEC = Grounding Electrode? - Is this the wire that runs from the panel to the meter?
Old 06-27-2011, 12:15 PM   #4
Master Electrician
Rewards Points: 3,870
Where is the main disconnect?
brric is online now   Reply With Quote
Old 06-27-2011, 12:16 PM   #5
The main disconnect is in the main panel - Shown on the right in my diagram
Old 06-27-2011, 12:30 PM   #6
rbj
So the meter does not have a main disconnect at the meter?
rbj is offline   Reply With Quote
Old 06-27-2011, 12:34 PM   #7
No, there is no disconnect at the meter... the only way to kill the power there is by physically removing the meter.
Old 06-27-2011, 12:41 PM   #8
rbj
The reason I ask is the panel in the pic is an MLO. The UFER GEC must be continuous #4awg to the main disconnect panel grounding terminal bar. The wiring diagram shows the meter by itself and should have a main disconnect combination.
Old 06-27-2011, 12:44 PM   #9
rbj
Pulling a live meter...ouch! I would suggest a main disconnect at the meter. Yer welcome...
Old 06-27-2011, 01:15 PM   #10
In case it matters... this is the existing electrical meter with a new main panel.
So since the meter doesn't have a disconnect, and there is a main disconnect on the panel and my UFER is continuous into the grounding terminal bar in the panel... is it wired correctly?
Or are you saying that I need to crimp the two grounds together and run it back to the meter as a "continuous" wire? Regardless if the meter has a disconnect.
Old 06-27-2011, 01:19 PM   #11
Electrical Contractor
jbfan's Avatar
Rewards Points: 478
Where is the disconnect for the panel?
Are you installing a backfed breaker?
jbfan is online now   Reply With Quote
Old 06-27-2011, 01:21 PM   #12
rbj
So there is a main disconnect at the panel shown in the pic now? If so then the cabling from the meter must be conduited to the MLO Where the #4 awg must go continuously to the UFER #4 rebar or Concrete encased electrode #6 or #4 electrode depending on what the service size is.
Old 06-27-2011, 01:32 PM   #13
Master Electrician
You must have a disconnect at the meter or at the panel unless you intend to have only six breakers in the panel. Normally there is no grounding conductor fromm the meter to the panel as per most utilities requirement--there are exceptions.
Old 06-27-2011, 02:28 PM   #14
See picture below. The disconnect is in the Main Panel (Shown as a red box)
Im not even sure what a backfed breaker is... so no, I'm not using one.
Old 06-27-2011, 02:35 PM   #15
Yes, see picture above. The main disconnect is in the Main Panel.
Sorry for being a little ignorant here but I'm going to break down your statement to make sure im following correct.y
From the Meter run the ground wire (through conduit) to my main panel (MLO)
and continue (without a break in the copper) into the UFER (#4 wire 20' encased in concrete)
Which mean, I need to splice the two ground wires in the panel pictured above?
The Following User Says Thank You to atmironov For This Useful Post:
Schlominator (10-02-2011)
Circuit Panel Question, neutral & ground bars ChrisDIY Electrical 32 02-14-2011 12:01 PM
Subpanel next to Main panel wired the same in 1990 Uncle Wayne Electrical 3 01-20-2011 12:43 AM
grounding of main panel and sub panel in older house linkysys Electrical 2 10-01-2009 04:34 PM
Quick question: No ground bar in panel? dawho1 Electrical 3 04-06-2008 10:17 AM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM