New GFCI Breaker Trips With No Load - Electrical - DIY Chatroom Home Improvement Forum
Old 04-06-2008, 07:08 PM   #1
New GFCI Breaker trips with no load
Just replaced a standard 15A breaker because three of the outlets on the circuit are in a bathrrom. The other four outlets are in an adjacent bedroom. With the old breaker (re)installed, I tested all outlets with a GRT-500 circuit tester - all show that they are correctly wired. Yet when I install the GFCI breaker, it trips instantly even with nothing plugged into any of the outlets. WHat am I missing?
bmurphywa is offline   Reply With Quote
Old 04-06-2008, 07:17 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
Is this circuit part of a multi-wire branch circuit (shared neutral)?
if not
Did you connect the circuit neutral to the breaker and the tail from the breaker to the neutral bar?
Speedy Petey is online now   Reply With Quote
Old 04-06-2008, 07:22 PM   #3
Thanks for your quick response. This circuit has its own neutral. That neutral (white wire) is attached to the GFCI breaker. The hot (black wire) is also attached to the breaker. The pigtail from the breaker is attached to the neutral strip inside the breaker panel. I think this is correct. Any thoughts? Thanks again.
Old 04-06-2008, 07:25 PM   #4
Go to each device on the circuit and check the wiring. You may have a white touching a neutral somewhere. This will instantly trip a GFI.
Old 04-06-2008, 07:32 PM   #5
OK. Just to make sure I understand your comment. You say a white touching a neutral - maybe I'm misunderstanding - I thought white was neutral. Am I looking for a white (neutral) touching a ground (bare copper)?
Old 04-06-2008, 08:37 PM   #6
Yes. A neutral touching ground on the load side of a GFI will trip it instantly.
Old 04-06-2008, 08:48 PM   #7
OK. I'm checking all outlets now.
New GFCI Breaker Tripping w/ 3-way Flourescents BigJimmy Electrical 8 12-29-2008 02:29 PM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 08:59 PM
20 Amp Breaker only trips once in a while panhandlion Electrical 14 11-26-2007 08:36 PM
Main Breaker Trips Repeatedly kkf Electrical 7 06-18-2007 04:31 PM
GFCI breaker problems bwoo Electrical 5 12-09-2006 02:53 PM