I'm going to try to be concise. I will most likely fail.
Got a new electric dryer. It replaced a gas dryer that was as old as the home ('93/'94) we think. The electrical service for a dryer appears to have been installed when the home was built. (The breaker for it, which has been off since we moved in a year and a half ago, is in the middle of the breaker panel with other original breakers installed below it.) The dryer is rated for 220V at 30A/breaker. The dryer repair guy stuck a clamp-around ammeter around both hot lines, one was pulling 20.5A and the other was 23.8 (after the dryer started up on the hottest setting). He said the dryer is fine. Both breakers are rated for 30A (according to the imprint on the end of the switch, and are two full-size connected breakers, as any 220 breaker setup should be. After the dryer has been on with Regular or Hot as the temp setting for a third of a cycle, the breakers will trip. Guaranteed. Immediately after tripping, the breakers are very hot to touch. The wire run between the 4-prong outlet and the breaker panel is 10/3 according to the shield on the wires connected to the breakers, and is run through conduit from panel to receptacle the entire way.
There.
After all that, should I replace the breakers, replace the plug, replace the 10/3, or replace the whole mess?
There.