Old 01-11-2009, 03:41 PM   #1
New Dryer is 3 wire, receptacle is 4 Wire.
Please Help,
My new Dryer is 3 Wire 240. Red, White, Black. 120/240 22a 60hz.
My receptacle is 4 wire 240 30a. Red, Black, Green, White.
I replaced the receptacle with a 3 wire using the 2 hots (red and black) and the non insulated (green). I capped of the white and plugged the dryer in.
It works fine but i occasionally get a shock from touching the dryer.
I am thinking since it says 120/240 i DO need that white neutral wire or some type of other ground to avoid this shock. (it has a digital display to select dry type and timer, im thinking this may need the 120 neutral wire?)
Any info is greatly appreciated.
-thanks eric
thelimit is offline   Reply With Quote
Old 01-11-2009, 03:45 PM   #2
DIYer
The neutral wouldn't be tied to the chassis anyway (would create parallel current paths), so you have a different fault.
Gigs is offline   Reply With Quote
Old 01-11-2009, 03:47 PM   #3
My License Ain't 4 Sale..
You need to put the 4-wire receptacle back in, and change the 3-prong cord to 4-prong. Find and disconnect the neutral to frame bond. Connect the green wire in the cord to the screw provided on the dryer.
This can kill you!
Old 01-11-2009, 03:57 PM   #4
Licensed electrician
You may want to verify the proper ampacity of your new dryer. Most are 30 amps wire with number 10 wire. You said yours is 15 amp.
If your really is 15 amp your breaker needs to be changed.
Old 01-11-2009, 04:04 PM   #5
Actually the dryer reads 22a. I am about to connect a 4 wire cord and use the 4 wire receptacle instead
Old 01-11-2009, 04:09 PM   #6
You need a 15 amp "double pole" breaker for this dryer.
rgsgww is offline   Reply With Quote
Old 01-11-2009, 05:13 PM   #7
can you elaborate why i would need a 15 amp double pole rather than a 30 amp double pole that i already have?
being that the dryer read 22 amp 15 amp should not work?
Old 01-11-2009, 05:30 PM   #8
The chassis is tied to the neutral in a 3-wire setup. This was how dryers were grounded since WWII.
Old 01-11-2009, 05:56 PM   #9
Sorry for the confusion, when I posted, your post about it being 22 amps was not shown.
The breaker there is fine. All you need to do is replace the cord with a 4 prong and the outlet back to 4 prong.
Old 01-11-2009, 06:08 PM   #10
If he goes to the 4 wire - wont he need to remove the jumper on the dryer too ? ( assuming it was even on ? ) ( see InPhase 277 post)
3 wire = Jumper connected
4 wire = Jumper Removed.
tribe_fan is offline   Reply With Quote
Old 01-11-2009, 06:12 PM   #11
THANKS FOR ALL THE HELP PROBLEM SOLVED
I switch to 4 wire and removed the neutral to ground jumper all is working well . amperage is 22 from dryer and my breaker is double pole 30a.
thanks again guys
Old 01-11-2009, 06:31 PM   #12
Electrician
thanks again guys
All the info you asked for should have been in your owners manual...
chris75 is offline   Reply With Quote
Old 01-12-2009, 09:24 AM   #13
Electrician's Helper
Pudge565's Avatar
Send a message via AIM to Pudge565
No he would not have to change the breaker. The breaker protects the wireing NOT the device. As long as the wire is 10 AWG a 30 amp breaker is fine.
There is no such thing as a stupid question, but there is such a thing as an ignorant person, with a question, trying to learn.
Pudge565 is offline   Reply With Quote
Old 01-12-2009, 09:34 AM   #14
DIYer
Why would it be this way in a dryer that was 120/240 and shocking him?!
Obviously this is a fault.
Old 01-12-2009, 11:31 AM   #15
It depends on the manufacturers specifications.
3 wire with ground to 3 prong dryer plug dgbunk Electrical 9 10-19-2010 02:07 PM
how to wire romex to 2 3 ways to a half hot receptacle smoothinstall Electrical 3 11-30-2008 11:56 PM
Should a dryer be 10 gauge wire & range 8/3? twilightcall Electrical 7 07-03-2008 07:29 AM
Dryer Grounding??? Traci_howdyadothat Electrical 7 05-27-2008 02:14 PM
Wiring a 220v dryer receptacle pjpjpjpj Electrical 8 06-05-2007 05:08 PM