New Detached Garage, Wiring, Questions - Electrical - DIY Chatroom Home Improvement Forum
Old 12-02-2008, 05:13 PM   #1
DIY
Rewards Points: 150
New detached garage, wiring, questions
I have some questions about my up coming garage wiring job. This will all be permitted and inspected and I'd rather not have the inspector laugh at me and make me re-do stuff
1) I have been assuming that I can put a maximum of 12 duplex receptacles on one 20 amp breaker. Is that actually correct?
2) I would like to have several welder outlets. These would be 240 volt, 50 amp, two conductor + ground. Can I put more than one on a breaker? Does that mean having accessible junction boxes to branch the circuit? Is it a good idea to use wire nuts on #6 CU conductors in this application?
3) I think I'll use #1 AL cable from the main panel in the house to the sub panel in the garage, underground (100 amp feed, about 50 feet total length). 1.5" conduit would be plenty for that, wouldn't it? What size would you actually use?
4) Is there any requirement or guideline for how close the ground rods need to be to the sub panel?
gp_wa is offline   Reply With Quote
Old 12-02-2008, 07:47 PM   #2
Rewards Points: 862
I may be wrong about this, but I believe a single receptacle (not duplex) of any type must be on it's own breaker.
Ultrarunner2017 is offline   Reply With Quote
Old 12-02-2008, 07:59 PM   #3
Electrician
Nope your wrong. But, if you do use a single receptacle on an individual branch circuit, it shall have an ampere rating not less than that of the branch circuit.
chris75 is offline   Reply With Quote
Old 12-03-2008, 04:07 PM   #4
DIY
Rewards Points: 150
Nobody?
Old 12-03-2008, 04:32 PM   #5
Originally Posted by gp_wa View Post
Nobody?
I wish I could help, I have been watching this thread as well to see the answers. Sometimes on this site, few people will answer the questions, then other times, you get tons of answers. I hope those electrical wizards will chime in for you.
737Pilot is offline   Reply With Quote
Old 12-03-2008, 09:44 PM   #6
could you post pictures of what you are doing. I am going to try and prewire my studio. Then have the electrician come out and do the dangerous work like connecting the wiring to the main house box( meter box I think). It almost sounds like something I am trying to do because my studio is detached and about 25 feet from the meter box on the house.
pauls is offline   Reply With Quote
Old 12-03-2008, 10:43 PM   #7
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
10 to 12 is reasonable. In the USA there is no maximum for general purpose branch circuits serving cord and plug equipment. You do have to use a little common sense.....
application?
Only one welder or more than one welder being used at one time?
It's about connected load...you can't run two welders requiring 50 amp branch circuits off one 50 amp double pole breaker. In general welder circuits are dedicated one welder in residential applications. You can use an extension cord made up to give you portability to different areas of the garage.
3 #1 al wet rated with a #6 al ground wire. 1 1/2" sch 40 is fine same for sch 80 where required.
No... locate them outside the drip edge of the roof and no closer than 6 feet to each other.
Washington requires 4 wire feeds to detached buildings with neutral and ground separated in the sub panel. This may require adding a ground bar . Use this diagram as a guide.....but you need to know what your doing and why or you will screw it up. You need a disconnecting means at the garage such as a main breaker sub panel immediately where the feeder comes into the garage. Some jurisdictions will allow a panel with no more than 6 breakers requiring no more than 6 throws of the hand as the disconnect. In this case a mlo panel is allowed or you may use a back fed breaker design utilizing a hold down kit on the main breaker.
Old 12-04-2008, 01:51 PM   #8
DIY
Rewards Points: 150
One at a time, it's just for flexibility. I've got an extension, but it's quite ridiculously large and unwieldy.
I know pretty well what I'm doing, but there are always a few little details I'm not sure I have worked out. I picked up a 200 amp QO 30 space panel with a main breaker, because hey, there's no such thing as too many spaces And I also got the add on ground bar.
Thanks for the help
Old 12-04-2008, 03:15 PM   #9
UAW SKILLED TRADES
Stubbie's Avatar
I'm glad you have a sense of humor.....
I'd say you are fine with your plan then. I'm not real sure how the inspector will approach several 50 amp welder receptacles on a single 50 amp breaker, you may have a little trouble getting him to buy it.
Other than that you look good on your knowledge of what is required so far.
You certainly will have enough spaces......
Old 12-04-2008, 04:10 PM   #10
Three #6 wires at each connection. That should be fun. I haven't seen any wire nuts rated for that. Time for these:
http://www.polarisconnectors.com/370...EXTRA_IPL1.pdf
jerryh3 is offline   Reply With Quote
Light Switch to Detached Garage - Grounding Issue smitty286 Electrical 1 10-22-2008 01:17 PM
help wiring detached garage to code ugabulldog Electrical 7 08-05-2008 09:48 AM
wiring detached garage ugabulldog Electrical 5 07-24-2008 05:13 PM
Wiring new detached garage/studio WShawn Electrical 4 07-21-2008 07:13 PM
Enhancing existing wiring to detached garage justinperkins Electrical 46 07-07-2008 08:29 PM