New AFCIs Always Tripping - Electrical - DIY Chatroom Home Improvement Forum
Old 07-02-2013, 09:38 PM   #1
Rewards Points: 83
New AFCIs always tripping
Helping a friend with some basement renovations, and part of it is 2 new circuits, one for receptacles and one for lights. Each circuit has a 15A AFCI breaker, both with fairly simple configurations (light circuit covers 6 recessed fixtures for 2 rooms, receptacle circuit is just for one room approx 12 x 18).
Got things all wired up nice and pretty, and each circuit trips as soon as any load is put on it (except for the lights in my receptacle tester). We tried multiple AFCIs with no luck on any, the circuits both work with standard breakers. Done multiple visual inspections of all of the lines and can't find any kinks, crossed lines, etc.
What are we missing in trouble shooting?
dvaupel is offline   Reply With Quote
Old 07-02-2013, 09:42 PM   #2
MarginallyQualified
Rewards Points: 2,464
Originally Posted by dvaupel View Post
Got things all wired up nice and pretty, and each circuit trips as soon as any load is put on it... What are we missing in trouble shooting?
It's called a megger.
http://lmgtfy.com/?q=megger+%2B+afci
Old 07-02-2013, 10:36 PM   #3
Resi EC
Rewards Points: 252
If it trips with only a load, could be the load, or a ground fault.
Try replacing the AFCI breaker with a GFCI breaker to test for ground fault, if it trips it will help narrow down the search.
If at first you don't succeed .... do not work on live electrical
Gac66610 is offline   Reply With Quote
The Following User Says Thank You to Gac66610 For This Useful Post:
MTN REMODEL LLC (07-02-2013)
Old 07-03-2013, 01:14 AM   #4
JOATMON
ddawg16's Avatar
Rewards Points: 1,810
Did you get the white ground wire on the AFCI properly connected to your neutral buss?
And....did you connect the neutral of the load to the AFCI? Not the neutral buss? Both the hot and neutral go to the AFCI.
Old 07-03-2013, 07:17 AM   #5
joed's Avatar
Rewards Points: 12,850
Start breaking the circuit apart. Disconnect half of it and see what happens. If it still trips then move closer to the panel. Repeat until you narrow down where the problem is.
Old 07-03-2013, 07:59 AM   #6
Licensed Pro
Tripping under load... it's either what ddawg said or you crossed the neutrals between the circuits.
The Following User Says Thank You to HouseHelper For This Useful Post:
Philly Master (07-03-2013)
Old 07-03-2013, 07:15 PM   #7
Electrical Contractor
kbsparky's Avatar
The neutral wire for the circuit MUST connect to the AFCI breaker, NOT the neutral bar.
Relocate it to the breaker.
-KB
Garage breaker keeps tripping rhanson85 Electrical 5 07-19-2012 06:24 AM