-   -   New AFCIs always tripping (http://www.diychatroom.com/f18/new-afcis-always-tripping-182961/)
dvaupel 07-02-2013 09:38 PM
Helping a friend with some basement renovations, and part of it is 2 new circuits, one for receptacles and one for lights. Each circuit has a 15A AFCI breaker, both with fairly simple configurations (light circuit covers 6 recessed fixtures for 2 rooms, receptacle circuit is just for one room approx 12 x 18).
Got things all wired up nice and pretty, and each circuit trips as soon as any load is put on it (except for the lights in my receptacle tester). We tried multiple AFCIs with no luck on any, the circuits both work with standard breakers. Done multiple visual inspections of all of the lines and can't find any kinks, crossed lines, etc.
What are we missing in trouble shooting?
TarheelTerp 07-02-2013 09:42 PM
Originally Posted by dvaupel (Post 1210775)
Got things all wired up nice and pretty, and each circuit trips as soon as any load is put on it... What are we missing in trouble shooting?
It's called a megger.
http://lmgtfy.com/?q=megger+%2B+afci
Gac66610 07-02-2013 10:36 PM
If it trips with only a load, could be the load, or a ground fault.
Try replacing the AFCI breaker with a GFCI breaker to test for ground fault, if it trips it will help narrow down the search.
ddawg16 07-03-2013 01:14 AM
Did you get the white ground wire on the AFCI properly connected to your neutral buss?
And....did you connect the neutral of the load to the AFCI? Not the neutral buss? Both the hot and neutral go to the AFCI.
joed 07-03-2013 07:17 AM
Start breaking the circuit apart. Disconnect half of it and see what happens. If it still trips then move closer to the panel. Repeat until you narrow down where the problem is.
HouseHelper 07-03-2013 07:59 AM
Tripping under load... it's either what ddawg said or you crossed the neutrals between the circuits.
kbsparky 07-03-2013 07:15 PM
The neutral wire for the circuit MUST connect to the AFCI breaker, NOT the neutral bar.
Relocate it to the breaker.