08-15-2010, 09:57 PM
#1
new 240 oulet...need troubleshooting help
hi...have a new 240 three prong 50 amp outlet (for lincoln a/c d/c welder)
wired from a 100 amp subpanel in my garage...
here's my problem...the welder won't work.....when i test the outlet, i get
120v in each leg, but nothing (no 240 v) when i try to multimeter the two hot legs together (i plug the welder in most of the way and then multitested the hot prongs)...multimeter reads "0" and a "-" (looks like a minus sign flashes)
i'm sure the subpanel is wired correctedly....ground and white are seperate in the sub...i have a double poll 40 amp breaker (one power switch) in the sub
i have two hots and a bare ground running from the subpanel to the outlet....i also have a white..unconnected to anything (just pulled it from the sub to the outlet just in case)....please note, my lincoln welder takes a three prong outlet...not the four...so i didn't use the white ..
gauge wire from the main to the house is 4....the gauge of wire from
subpanel to outlet is 6 (except 12 for bare ground)
sorry if this sounds confusing, but i am consused!
08-15-2010, 10:05 PM
#2
Licensed electrician
Is this powered by a two pole breaker or a tandem breaker?
A tandem breaker only supplies 120 volt power to two circuits, not 240 to one circuit.
08-15-2010, 10:16 PM
#3
A tandem breaker only supplies 120 volt power to two circuits, not 140 to one circuit.
double pole..just like this one...thanks for the response
GE Model # THQL2140
http://www.homedepot.com/webapp/wcs/...02&marketID=48
08-15-2010, 10:22 PM
#4
Electrician
Measure the two termination points of the breaker and see what you are getting.
Check all connections. It is possible that one of the hots is loose and you are reading phantom voltage when metering it to ground.
Anything fun is either illegal, immoral, or fattening.
08-15-2010, 10:26 PM
#5
are the termination points where the wire is connected to the breaker?
by the way...when i use a voltage detector, both the outlet and the wire from the welder (when plugged in)
suggests there is voltage/hot...by the way, i'm sure the welder works..i tested it in another outlet
08-15-2010, 10:45 PM
#6
Electrician
Yes.
We know there is one hot, we are trying to figure out why the other one isn't working.
The welder isn't the problem, the leg that is reading 120V to ground but 0 to the other leg is the problem.
08-15-2010, 11:00 PM
#7
Yes.
thanks prody.....i hope i explained it correctly....each hot side is reading 120 v when grounded....but can't get 240v between them.....hope i'm not being redundant...thanks for your time and help in trying to help me figure this out....have an old alfa my father and i are trying to restore
08-15-2010, 11:23 PM
#8
Electrician
So you are saying that you measured the two terminals of the 2-pole breaker and you do not get 240V between them?
If that is true, then you have to check the sub panel. Whatever it is fed with, either by main lug or main breaker, you have to check this and see if you get 240V between the two.
The Following User Says Thank You to Proby For This Useful Post:
08-15-2010, 11:43 PM
#9
Wire Chewer
I know with my panel, I can't just put a double pole breaker anywhere in it. They legs are not staggered at every circuit. If you get 0 volts from both screws, test from one screw to the breaker below or above, to see if you get 240. If you do, you'll want to move it up or down a notch.
The Following User Says Thank You to Red Squirrel For This Useful Post:
08-15-2010, 11:52 PM
#10
thanks..i'll check first thing tomorrow
it's a ge subpanel box...forgot the model, but labeled subpanel with
100 amp breaker and a few 20 amps in it
08-15-2010, 11:58 PM
#11
just found the model #
GE DEH-40537
hopefully i can put double breakers in it
08-16-2010, 12:16 AM
#12
ok..will do...just ran out in the dark and thought the mail lugs also read zero with the "-"...but just a quick check..i'll be more exact tomorrow
by the way..the three 20 amps circuits in my garage work fine from this subpanel
08-16-2010, 12:26 AM
#13
when using a multimeter:
to check the box...or breaker in the box...do i place the hot on the breaker or lug and the black on a ground?..
08-16-2010, 01:04 AM
#14
It does not matter which lead is placed on the hot or ground.
08-16-2010, 07:43 AM
#15
Electrical Contractor
Check the placement of the breaker.
Ge panels are made so the whole panel with accept the thin breakers, and sometime you can put a thin 2 pole breaker into a single pole slot.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
| Thread Tools |
Search this Thread |
| Display Modes |
Linear Mode