#1 |
Neutrals Question...
I just got 2 deep fryers for the pool deck. They are 110v. I realized late that the amp draw for them would be too much for a single duplex outlet on a 20 amp circuit. I was able to break the tab on the outlet and use a spare conductor to have two 110v 20a circuits, one to top and one to bottom of outlet. My question is this... I only have the one neutral in the j-box. will it be overloaded or will it be fine. I hate to have to bring another neutral to the box as it will require wall demolition and that includes some nice tile work. Currently (no pun intended) I have one neutral going to combined/adjoined side of the duplex, and 2 conductors going to the 2 hot screws with the 2 outlets separated on the hot side only.
Brent |
#2 |
It will be fine if the two hots are connected to a double pole 240 volt breaker to get 240 volts between the hots. In this case the neutral will only carry to current difference between the hots.
All three conductors must be in the same cable as well. You can't just grab a hot wire from another circuit.
Do not PM with questions that can be asked in a forum. I will not respond. |
#3 |
Licensed electrician
This just got to be a very expensive endeavor if the receptacle is outside. Outside receptacles need to be GFI protected. Double pole GFI breakers are not cheap. You cannot use a GFI receptacle on two circuits like you have.
Answers based on the National Electrical Code. Local amendments may apply. Check with your local building officials. |
#4 |
Why a double pole 240v breaker? Why not use the 2) 20a 110v breakers? One half of the duplex is on one 20a 110v and the other is on a another... I have 2 fryers consuming 15 or so amps each. The house is custom and no Romex used... We spec'ed EMT and nothing under 12 awg and 20a breakers thru out. The conduit had one neutral from the panel and 3 conductors. I was able to add a another conductor from a very little used circuit to this duplex but adding another neutral would still be feeding from the one in the attic j-box from the panel.
Brent |
#5 |
The NEC requires that multiwire branch circuit have a common means of disconnect. A two pole breaker also ensures that the circuits are on opposite legs of the panel to avoid overloading the neutral.
How far are these receptacles away from the water?
#6 |
Should have been more clear... The "deck" is considered "dry" as I have a second set of sliding glass doors to close off the elevated recreation area from the pool deck. No outlet is within 30+ feet of a water source.
All the "double pole breakers" I see have both halves on the same hot "bar". So what creates the neutral overload? In theory only... does the neutral see higher amps if both circuits are on the left or right hot leg? Would it be reduced if one circuit is on the left bar and the other on the right? Thanks again, Brent |
#7 | ||
You talking to me?
Neutrals Question...Quote:
#8 | |
Then attach the second neutral to the same half of duplex receptacle as the matching hot and break off the tab between the neutral screws also. Neutrals from two different sources are not tied together in an outlet box or junction box.
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded. |
#9 | |
Xtreme DIY'r
No closer then 6' 680.22 One thing my Inspector noted I needed to fix I had an outlet just outside the pool area The outlet is supposedly so that no-one will need to run extension cords I've actually installed 4 outlets along 2 sides of the pool for general use No closer then 10' to the pool |
#10 | |
You talking to me?
If you use circuits from the same leg of the panel, the current is additive so having 2 20 amp circuits, you could end up with 40 amps of current on the neutral. |
#11 |
" Euro " electrician
There are couple items it have to be addressed .,
All outdoor receptales must have RCD { GFCI } it do not matter if single circuit or MWBC { MultiWire Branch Circuit } { pay attetion to the 2008 NEC code they change a bit on this one all the 240 volt outdoor circuit are now required it I know you will say Eh ? but they change that on Pool/ Spa part so it carried over to outdoors receptales as well }Second thing with MWBC you must have same netural as two hot circuits no grabbing from somewhere else. I know you mention conduit so that is the best route to pull in new MWBC you can not run split receptale at all on outdoor unless you have RCD breaker for it. otherwise run new hot and netural on seperated circuit and add second RCD receptale next to the first one that is one of few legit way you can deal with it. Oh yeah I hope you have fire extisghener in your area due you have deep fryers. If you have GE load centre they are little tricky to deal with it. If that the case we will give you a special instruction how dealt with it. Merci. Marc |
| Display Modes | |
| Multiple neutrals for same circuit | ericdube | Electrical | 2 | 07-19-2009 12:54 AM |
| A question about water preassure. | reasonforseason | Plumbing | 5 | 04-14-2009 05:36 PM |
| GFCI feeing subpanel question | scott2332 | Electrical | 45 | 02-28-2009 04:15 PM |
| Electrical Panel "cut-in" question | Todd-sta | Electrical | 52 | 12-04-2008 12:07 AM |
| Basement Renovation Question | KUIPORNG | Remodeling | 234 | 08-26-2008 09:19 AM |