Neutral And Ground Wires - Electrical - DIY Chatroom Home Improvement Forum
Old 04-17-2011, 11:26 AM   #1
neutral and ground wires
a little help understanding this if the three feeder wires coming into home panel 2 hot 1 neautral why is it that it is said neutral is like ground wire because it is not hot. I thought the neutral was the wire the electricity returns on so that should be live i am confused can someone explain
. also why cant you bond neutral and ground at a subpanel?
Tony vargas is offline   Reply With Quote
Old 04-17-2011, 11:33 AM   #2
Rewards Points: 81
The neutral is the return path for the electricity to flow. So when you check for voltage on a and b in a home you have 240 but when you got from a to neutral you have 120 and b to neutral you have 120. In a sub panel the neutral and grounds must be seperate because all grounding must be done back at the main panel ( this is a rule). If the neutral conductor in
the subpanel ever became disconnected, anything that was grounded would
become a shock hazard as the grounding conductor would now carry the neutral current.
Chevyman30571 is offline   Reply With Quote
Old 04-17-2011, 01:29 PM   #3
Civil Engineer
Rewards Points: 4,690
The neutral does carry current under most conditions, however the voltage potential of the neutral is the same as ground (generally assumed to be 0 volt potential) because the neutral is connected to the ground wire at the panel. In theory, since the neutral is at the same potential as ground, if you touch the neutral with your hand, and you are grounded, you would not get a shock because the neutral is at ground potential, you are at ground potential, hence no current flow through you (V/R = I) where V is the voltage potential difference in volts, R is the resistance in ohms, and I is the current flow in amps.
However, it would be a VERY BAD IDEA to try this in practice, because the neutral may not be at ground potential, and the "ground" you are touching may be at a different potential than the neutral ground. Under those conditions, it would be entirely possible to get a shock by touching the neutral.
Old 04-17-2011, 01:34 PM   #4
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
It can be done using a voltmeter though.
Old 04-17-2011, 03:07 PM   #5
Thanks guys good answers i believe i have a much better understanding now i appreciate it,
Old 04-17-2011, 05:32 PM   #6
I=E/R
a7ecorsair's Avatar
It isn't really the return path any more than the Hot side is the supply. It is just one connection to the secondary side of a transformer that just happens to be earth referenced. AC current flows both ways in the neutral just as it does in the hot connection.
a7ecorsair is offline   Reply With Quote
3 Wire Set Up . . . Neutral Wire Tied to Ground Wires irishMonster Electrical 14 10-21-2010 08:20 AM
Sharing Neutrals on the same phase electro Electrical 30 08-12-2010 02:10 PM
240 volt load/appliance and ground vs neutral kgize Electrical 7 04-22-2010 11:40 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 04:58 PM
Subpanel feeder questions Silhanek Electrical 4 03-22-2007 06:30 PM