When putting an amprobe(tester) on a neutral should it generate current? If not what does that indicate?? Thanks
Mstrlucky74 is offline   Reply With Quote
Old 12-24-2013, 04:24 PM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,032
On a 120 volt circuit, the neutral current is the same as the ungrounded conductor (the hot). If it is not you have a ground fault.
Coastal South Carolina
Old 12-24-2013, 05:03 PM   #3
Rewards Points: 874
Well all the neutrals in my panel don't make the tester go off....the hots obviously do...??
Old 12-24-2013, 05:24 PM   #4
is this a branch circuit neutral? a neutral for a 240v feeder? a neutral on a mwbc?
itsnotrequired is offline   Reply With Quote
Old 12-24-2013, 05:47 PM   #5
Master Electrician
Rewards Points: 3,678
Is it an amp probe or non-contact voltage tester. Voltage and current are not the same thing. An NCV tester does not register on grounded conductors(neutrals).
brric is online now   Reply With Quote
The Following 3 Users Say Thank You to brric For This Useful Post:
k_buz (12-24-2013), mpoulton (12-28-2013), plummen (12-24-2013)
Old 12-24-2013, 06:07 PM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
"Go off" ???
You are talking about voltage, not current.
Current is amperage, or flow of current, and is present on both the hot(s) and neutral.
Voltage is the push and is only present on the hot conductor(s).
Think in terms of water pipes.
Voltage is the water pressure.
Current is the volume or water flowing.
The Following 3 Users Say Thank You to Speedy Petey For This Useful Post:
ddawg16 (12-24-2013), mpoulton (12-28-2013), Mstrlucky74 (12-26-2013)
Old 12-24-2013, 06:49 PM   #7
Rewards Points: 874
A NCV tester. Here it is. Thanks.
http://www.mymeterstore.com/p3166/am...and_shaker.php
Old 12-24-2013, 06:55 PM   #8
Rewards Points: 774
Utilizing an amp clamp commonly called an Amp-probe
On a 120 VAC 2 wire circuit with a ground
If you have 7 amps on the ungrounded conductor (HOT), you should have 7 amps on the grounded conductor (neutral/common/white)
On a 120 VAC 3 wire (multi wire branch circuit) 2 ungrounded conductors (typically black and red) with a neutral. If you have 7 amps on Black,7 amps on red you should have "0" (zero) amps on the neutral
On a 120 VAC 3 wire (multi wire branch circuit MWBC) 2 ungrounded conductors (typically black and red) with a neutral. If you have 7 amps on Black and 5 amps on red you should have 2 amps on the neutral
At all times you should have "0" (Zero) amps on the ground conductor.
If you take your amp clamp and encompass all the conductors (excluding the ground conductor), both conductors of a 2-wire circuit or all three in a MWBC you will read or should read "0" (Zero) amps. If you read anything beside "0" amps you have a wiring issue.
Know A Little is offline   Reply With Quote
The Following User Says Thank You to Know A Little For This Useful Post:
Old 12-26-2013, 07:28 AM   #9
Rewards Points: 712
That is true, ONLY if you do not have harmonic loads.
Mark
busman is offline   Reply With Quote
Old 12-27-2013, 06:47 PM   #10
Rewards Points: 774
Mark
The AVERAGE DIY'er is utilizing single phase 240/120 and 3rd harmonics are not an issue.
Hot appliance due to jumpering receptacle neutral to ground screw justplumducky Electrical 6 07-09-2013 06:52 AM
AFCI Breakers Keep Tripping mopowers Electrical 12 09-04-2009 04:11 PM
Electrical connections TazinCR Electrical 11 01-07-2009 08:10 PM
Help if it's not too late!! Cyndi Electrical 255 10-10-2008 10:18 PM
Ground question. mystery guest Electrical 5 07-24-2008 01:47 PM