Neutral The Controlling Conductor? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-13-2012, 06:15 PM   #1
neutral the controlling conductor?
Greetings To All:
There should never be any instance with residental house wiring in the State of New Jersey where the neutral (white) conductor is run through a switch to control any electrical device. Correct?
This is an unsafe, dangerous and should be corrected immediaetly. Right?
Upon discovering this situation the device has been put out of service.
After all of your learned and experienced answers the plan is to have this remedied by this week's end, if you say so.
Regards,
fish96
FISH96 is offline   Reply With Quote
Old 05-13-2012, 06:50 PM   #2
Code05's Avatar
Rewards Points: 1,104
Does not matter what state you are, I do not know of any jurisdiction amends this. Note the exception though
404.2 Switch Connections.
(A) Three-Way and Four-Way Switches. Three-way and
four-way switches shall be wired so that all switching is
done only in the ungrounded circuit conductor. Where in
metal raceways or metal-armored cables, wiring between
switches and outlets shall be in accordance with 300.20(A).
Exception: Switch loops shall not require a grounded
conductor.
(B) Grounded Conductors. Switches or circuit breakers
shall not disconnect the grounded conductor of a circuit.
Exception: A switch or circuit breaker shall be permitted
to disconnect a grounded circuit conductor where all circuit
conductors are disconnected simultaneously, or where
the device is arranged so that the grounded conductor cannot
be disconnected until all the ungrounded conductors of
the circuit have been disconnected.
Code05 is offline   Reply With Quote
Old 05-13-2012, 07:13 PM   #3
Pure Genius
Rewards Points: 150
Can you show a pic of the switch? Is the wiring knob and tube? It was common practice in those days to switch the neutral
Dierte is offline   Reply With Quote
Old 05-13-2012, 07:16 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
Originally Posted by FISH96 View Post
Greetings To All:
Regards,
fish96
Who are you taking to??
Are we missing something?
Speedy Petey is online now   Reply With Quote
Old 05-13-2012, 07:30 PM   #5
Idiot Emeritus
Rewards Points: 1,492
Just because the wire is white doesn't mean it's a neutral.
If a two-wire cable is run from a ceiling box down to a switch box, it'll have a black and a white. In this case, it's required to use the white as the hot and the black as the switch leg.
You're supposed to identify the white as a hot, but in my experience, this isn't done very often.
Rob
micromind is offline   Reply With Quote
Old 05-13-2012, 07:55 PM   #6
neutral the controling conductor?
greetings to all who replied so far:
it is a simple on off switch. the neutra(white conductor)l is wired to the switch to control the energizing of the device.
to speedy peety i have spoken to no no one i discovered this situation while effecting maintenance on the appliance.
i am taking all comments as this situation is not code and should be changed to the hot( black conductor) throught the switch.
i had confirmed with great effort that black is hot and white is 'solid neutral' in this circuit
regards and thank you to all
fish96
Old 05-13-2012, 08:23 PM   #7
Electrical Contractor
jbfan's Avatar
Rewards Points: 142
How many wires in the box, and what wires are on the switch?
Old 05-13-2012, 09:12 PM   #8
hello all.,
there are three conductors in the box, black (hot), white ( neutral) and bare ground.
the only conductor on the switch is white( neutral) in and out. the connections are on oppisite sides of the switch.
i suspect something is amiss as the ground condutor is spliced with a wire nut. i believe this contavenes all NEC's as the splice should be formed with a copper crimp connector expressly for this purpose.
thanks all,
fish96
Old 05-13-2012, 09:26 PM   #9
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If there are 2 conductors [+ground] in the box and only the white goes to the switch, then the switch wouldn't do anything.
Old 05-13-2012, 09:27 PM   #10
Rewards Points: 6,652
Sounds like someone copied and pasted directly from their homework.
Old 05-13-2012, 09:29 PM   #11
Yes. They are copying and pasting directly from their homework, or are a foreigner and having someone translate to the site, so they can have everyone do their homework for them.
Old 05-14-2012, 06:06 AM   #12
Greetings:
i am not a faking this.i am not cutting and pasting from a homework assignment, this is a legit concern with what i have discovered in my home.
so is the use of the white wire thru a switch to control the operation of an appliance/device code? three wires black, white, ground are in the box white thru the switch.
i do not know why my previous posts aroused any concerns of fakery.
regards,
fish96
Old 05-14-2012, 06:30 AM   #13
Sparky
Rewards Points: 510
if there are only 3 wires (1 cable) in the switch box, the white is NOT a neutral, but *should* have been re-identified as a hot wire
Techy is offline   Reply With Quote
Old 05-14-2012, 06:39 AM   #14
This.
Like micromind said, just because the wire is white doesn't mean it's a neutral.
The Following User Says Thank You to Speedy Petey For This Useful Post:
gregzoll (05-14-2012)
Old 05-14-2012, 07:06 AM   #15
Rewards Points: 1,418
It is okay to use wire nuts for the (bare and/or green) ground wires.
Twisting with no crimp and no wire nut is nowadays not considered good enough.
...there are three conductors in the box, black (hot), white ( neutral) and bare ground.
Does it work?
Where does the black wire go?
When a single cable with 2 conductors with ground is the only wiring in the switch box and goes up to where the power and the light are, you correctly connect the black wire to one switch terminal and the white wire to the other. Up where the light is you connect the black wire to the light or receptacle hot terminal and the white wire to the single black or cluster of black wires for the power. Both ends of that white wire should be marked with a black or red band of tape or stain. Other, incorrect, connections may result in a short circuit that trips the breaker and might damage the switch
It looked like you were answering someone else's question instead of asking your own, except no one else had asked the question.
The Following User Says Thank You to AllanJ For This Useful Post:
Speedy Petey (05-14-2012)
Why can't you connect Ground/Neutral bus bars on a sub secutanudu Electrical 42 11-07-2012 02:33 PM
Need Neutral Connections - Installing Subpanel ctlu008 Electrical 10 01-01-2012 08:54 AM
upping neutral and ground conductors for multiple circuits crankcase Electrical 2 03-18-2011 01:37 PM
Electrical connections TazinCR Electrical 11 01-07-2009 08:10 PM
Suspected open/loose service neutral mrtomwj Electrical 5 09-28-2006 09:46 AM