Need A Ruling! - Electrical - DIY Chatroom Home Improvement Forum
Old 05-03-2011, 07:44 PM   #1
Rewards Points: 12
Need a ruling!
I have a 100 amp panel in the garage that has two circuits that are 30 amp for a old welder the previous owner had. There is one 10/3 that runs from the panel to the first outlet. Then a line that runs from the first outlet to the second outlet.
Seems one breaker is using the black wire as hot and the second breaker is using the red wire as hot and I think both are sharing the same neutral.
First question is that ok?
Second, I want to change the plugs to 50 amp plugs and also change the breakers to 50 amp - I read somewhere that as long as I marked the outlets "For Welder Use Only" it was acceptable by code. Is this ok?
thesmackdown is offline   Reply With Quote
Old 05-03-2011, 08:03 PM   #2
licensed electrician
This is acceptable provided the breakers are on different phases, you can't share a neutral with two circuits being fed from the same phase. You can change the plugs and the breakers but you will need to to up size the wire to #6 as #10 is only good for 30A
The Deez is offline   Reply With Quote
Old 05-03-2011, 09:43 PM   #3
Rewards Points: 12
OK so maybe I should go back to square one. This is what the manual for the welder says:
3.04 Electrical Input Requirements
Plug the input cord into a properly grounded and protected
(fuse or circuit breaker) mains receptacle capable of
handling a minimum of 20 Amperes. The Fabricator 131
requires a 115VAC supply Voltage, the Fabricator 181
requires a 230VAC supply Voltage.
The Fabricator 131ís power cord is equipped with a NEMA
5-15P plug and will only connect to a NEMA 5-15P
receptacle.
The Fabricator 181ís power cord is equipped with a NEMA
6-50P plug and will only connect to a NEMA 6-50P
receptacle.
I have the Fabricator 181 - do I just need to change out the outlet to a 6-50P?
Old 05-03-2011, 09:47 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,864
This is more than likely legal, but I DO NOT like to do this in a residential setting.
Most home based welders (people, not machines) do not care about duty cycle, and the next owner of the house is not going to care if it says "welder use only". They will plug in their kiln either way.
Old 05-03-2011, 09:55 PM   #5
Rewards Points: 12
So, I should do the breakers and the plugs? Or just the plug based on the information from the manual?
Old 05-03-2011, 10:03 PM   #6
the receptical you need is a NEMA 6-50R. which is a 50A 250V 3 wire. I still don't think that is legal, but maybe it is. IMO in this case the wire should be sized to match the size of the breaker your feeding the equipment with, the breaker is to protect the wire, not the equipment. being a resi situation like pete said, this is the best way to go. commercial and industrial applications are a little diff.
Old 05-03-2011, 10:04 PM   #7
just the plug, you can feed #10's with a 30amp 2pole breaker, leave the breaker alone unless it trips out, then change the wire and the breaker
Old 05-03-2011, 11:13 PM   #8
Rewards Points: 12
On a earlier point. To use two welders at the same time do the breakers need to be on different phases?
Right now they are both on the same side.
Old 05-03-2011, 11:15 PM   #9
I ask the impossible!
Rewards Points: 640
Just to be sure it's clear, changing the plug should be okay. Changing the breaker should only be done if you change the wire.
Please do NOT consider any "before" picture of my house as any kind of endorsement of any particular construction method. In fact, you should probably assume that if I post a "before" picture, I am posting it because I am soliciting advice on a proper replacement for one of MANY things done wrong by a previous owner.
WillK is offline   Reply With Quote
Old 05-03-2011, 11:17 PM   #10
Rewards Points: 12
Thanks for making it totally clear!
Old 05-03-2011, 11:42 PM   #11
Scared Electrician
Saturday Cowboy's Avatar
most panels the phases are located on every other row. 1st row A phase 2nd row B phase, etc.
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
Old 05-03-2011, 11:52 PM   #12
Rewards Points: 640
So on that question I'm a little confused about what you're saying. You're using a 230V welder or welders. These are going to use 2 hot wires and 1 neutral, so you're running off a 30A double pole breaker and as such you're using both phases of the electric service for each welder.
Old 05-04-2011, 12:13 AM   #13
Rewards Points: 12
Nope, both welders are single phase. The breakers look to be standard 30A breakers. Is that not going to work?
Old 05-04-2011, 12:18 AM   #14
Rewards Points: 1,016
The 30a breaker and #10 wire will most likely be fine for that welder. I have a Miller 180 MIG welder on similar circuit. Rather than install a welder recep I installed the more common recep so I can readily plug in other equipment. Then I made an longer extension cable for the welder with conversion plug and recep. Works great.
____________
Vince
Old 05-04-2011, 12:23 AM   #15
Rewards Points: 12
Good idea as I was going to make up an extension cord anyway.
We are also going to run a Thermal Arc ArcMaster 185 at the same time (a friend is coming to do some welding training).