Need To Install A Sub-panel In The Garage - Electrical - DIY Chatroom Home Improvement Forum
Old 02-11-2009, 08:05 PM   #1
Need to install a sub-panel in the garage
Need to install a sub-panel in the garage and I would like to know what conduit to use from the house to garage that can be buried?
That gray pvc or flexable liquid tight? Whats legal in Ca?
serrano is offline   Reply With Quote
Old 02-11-2009, 08:23 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 546
Need much more info than that!
Old 02-11-2009, 08:50 PM   #3
Ok, lets start here.....
It's a house build in 1957-single story-raised foundation with a 200 amp panel in the laundry room. All the walls are down to stud for easy access.
We have a friend that said he could install a 100amp panel in the garage but I'd like to know what the correct way to get from A-B would be when going underground?
Need more info?
Thanks.
Old 02-11-2009, 10:48 PM   #4
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Schedule 40 gray PVC 18" deep under ground. Schedule 80 while above ground going to the panels. You need to run 4 wires 2 hots, one neutral and a ground. You need a single throw main disconnect at the detached garage. For 100 amps not considering any long distances panel to panel for voltage drop you need #3 copper or #1 aluminum for the hots and neutral and a # 8 copper or # 6 aluminum for equipment ground. the 100 amp disconnect or 100 amp main breaker panel must be located at the point of entrance of the feeder to the detached garage either outside (3r enclosure) or inside. Make it look like this with neutral an ground electrically isolated. You may need to purchase a ground bar kit to do this depending on the panel but neutrals and equipment grounds will not be on the same bar and you will not install the main bonding jumper. You will also need a ground rod and grounding clamp with the grounding conductor connected to the sub-panel ground bar.
Make it look like this......this diagramis a guide.. it is not intended to be a substitute for electrical knowledge and common sense.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
Garage Wiring issues jimmyfloyd Electrical 20 06-08-2009 02:57 PM
Sub Panel SoxFan Electrical 2 12-02-2008 10:16 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM