Need help rigging 30 amp
So.... I have a jacuzzi shower unit that is rated at 3000 watts / 27.3 amps. But the romex is run and drywall/paint finished. No way can i run 100' of 10awg now.
But I do have two runs of 12awg available. I know its not code. So this will be rigging. Is it possible to pair up the two 12awg to a single 30 amp outlet? |
Btw, each 12awg is connected to a 20 amp gfci breaker.
With no way to run a new cable as you stated you will not be using the tub. Sorry.
You cannot parallel conductors that small. |
Thanks. There is no turning back on the tub either. I'll just use it at 20 amp and reset the breaker whenever it fails.
You're right...it's not code. And I don't think any electrician on this site would advise that you do what you propose. Our advise is to do it safely and correctly, and that means installing the correct wire gauge/branch circuit material as recommended by the manufacturer.
How about this rig job? Replace the two 20 amp gfci's with a single 20 amp 2-pole gfci. Then have two 20 amp gfci outlets.
Then splice two plugs onto the tubs power cord and plug each into it's own outlet? I know it's wrong. Just asking for help choosing the least wrong of all the wrong choices. |
Sorry...wrong is still wrong. 1% wrong is just as bad as 100% wrong.
This is said in jest. I in no way advocate trying to circumvent safety. |
Do you even realize what is at stake?????? :icon_rolleyes: WHY in the world would something rated at 3000 watts be made to run at 120V??? Can you exchange the steam unit alone? |
Wire up one of your #12 cables for 240 Volts. Then install a 3 kVA 240x120 transformer, and change it back to 120 Volts at the shower connection. Problem solved.
Why is it impossible to run new wire???!!?? It can be done with little or no drywall damage. What is the nature of the house construction and where is the panel?
Paralleing Conductors
I highly recommend you to even go to size 8 AWG to assure a good life for your cable for long time trouble free usage. I do not recommend at all to use parallel runs of cables. If it is attended, short cycles usages with parallel conductor requirements by local codes such as equal length, sizes etc. and the fact that you would guarantee no breakage of system under load at terminals or between, then I believe you could use. Make sure that the cable is not run in a combustible area either. Use a timer that is good and operative could guarantee disconnection after some time. |
In one breath you say it can be done, then you say you would never recommend it, then you go on to explain how it can be done. What is your story??? |
I did something similar once with three plugs, one for each phase on a 3-phase system. That was in a high-voltage physics lab with 12,000-volt transformers, and it was still a dangerously bad idea. Quote:
| All times are GMT -4. The time now is 09:15 AM. |