Does anyone happen to know the NEC section that covers isolating neutrals from grounds in subpanels?
Having a discussion with someone and I can't find it. Thanks!
Andrew
secutanudu is offline   Reply With Quote
Old 12-13-2012, 10:46 AM   #2
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
250.32 (b)(1)for buildings or structures detached from the structure or building with the service equipment.
250.24(a)(5) for load side of service equipment.
Note prior to 1996 code cycle you were allowed to bond a 3 wire feeder to a detached structure or building. There are many thousands of those existing today, especially in farm and rural settings. Not to mention the 3 wire dryer and ranges out there.
Old 12-13-2012, 08:58 PM   #3
Just call me Andrew
What about for attached subpanels? Is there any code stipulation? Thanks.
Andrew
Old 12-13-2012, 09:54 PM   #4
Licensed electrician
Do you mean in the same building as the service?
Old 12-13-2012, 09:56 PM   #5
Just call me Andrew
Exactly, Jim. Sorry.
Andrew
Old 12-13-2012, 10:04 PM   #6
They have always required a 4 wire feeder and isolated neutrals and grounds as long as I know.
The exception was to a detached structure as was already mentioned. This was allowed only if there were no metallic paths between the structures like a water line, phone or cable etc.
Old 12-13-2012, 10:07 PM   #7
Just call me Andrew
Which code article describes the NEED for the isolated ground?
Andrew
Old 12-13-2012, 10:13 PM   #8
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
250.24 (a)(5)
load-side grounding connections. A grounded conductor
shall not be connected to normally non–currentcarrying
metal parts of equipment, to equipment grounding
conductor(s), or be reconnected to ground on the load side
of the service disconnecting means except as otherwise permitted
in this article.
Generator connection – Question - Final Plan Apollo67 Electrical 24 01-30-2012 08:44 PM
Ground to Neutral jumper found in house kennedy1209 Electrical 8 02-08-2011 07:10 AM
3 Wire Set Up . . . Neutral Wire Tied to Ground Wires irishMonster Electrical 14 10-21-2010 09:20 AM
Hot Tub Install--Grounding Rod Question statgeek_rob Electrical 16 09-15-2007 03:59 AM
Subpanel feeder questions Silhanek Electrical 4 03-22-2007 07:30 PM